Dear All
If you are experience or had facing this issue the same . Please kindly share solution to solve this issue
We are using PLC of Honeywell with the model Control Edge HC900, it was installed 10 years ago. Recently, we are facing big issue on the paper machine as CPU auto reset and start within 3s and happened with high frequency ( 5 times/day ).We tried to execute many step to separate this system , but it is still happening with more high frequency . Till now I don't know what we will do to solve this issue
Our solution was executed . We have 4 cracks
1. Change new CPU
2. Change new crack for CPU
3. Replace and move AI/AO module on the crack of CPU to other crack
4. Separated some signal such as AI/AO
Note :
Even through we taken all module and just CPU HC900 C70 on this crack . The problem still happened .
Do you think this problem cause by noise from grounding
- We measure current with the cable of the grounding for all cable to connect with the controller such as DI,DO, AI,AO is 1.7 A. With this value whether impact to reboot the CPU of HC900 or not ? How much limited leakage current for this HC900 C70 ?
Thanks
If you are experience or had facing this issue the same . Please kindly share solution to solve this issue
We are using PLC of Honeywell with the model Control Edge HC900, it was installed 10 years ago. Recently, we are facing big issue on the paper machine as CPU auto reset and start within 3s and happened with high frequency ( 5 times/day ).We tried to execute many step to separate this system , but it is still happening with more high frequency . Till now I don't know what we will do to solve this issue
Our solution was executed . We have 4 cracks
1. Change new CPU
2. Change new crack for CPU
3. Replace and move AI/AO module on the crack of CPU to other crack
4. Separated some signal such as AI/AO
Note :
Even through we taken all module and just CPU HC900 C70 on this crack . The problem still happened .
Do you think this problem cause by noise from grounding
- We measure current with the cable of the grounding for all cable to connect with the controller such as DI,DO, AI,AO is 1.7 A. With this value whether impact to reboot the CPU of HC900 or not ? How much limited leakage current for this HC900 C70 ?
Thanks