How can we equalize the ground fault in ground fault current with open delta voltage?
A generator is protected by a ground fault CT of 200/5 set to 2.5A secondary. When synchronized with grid the NGR switched off and the only protection of ground fault depends on open delta PT 11KV/110V. Somebody can guide how much secondary voltage of open delta would be equal to 2.5A secondary fault current of CT?
Regards
Shaheed
A generator is protected by a ground fault CT of 200/5 set to 2.5A secondary. When synchronized with grid the NGR switched off and the only protection of ground fault depends on open delta PT 11KV/110V. Somebody can guide how much secondary voltage of open delta would be equal to 2.5A secondary fault current of CT?