R
The running indication on the DCS was missing while the machine was running - this was the complaint. Technician went and found a relay that receives a signal through CB auxiliary did not energize. He racked out the CB and applied "CRC lectra Clean" to clean the LV plug and socket and then racked in into the service.
The motor was started but no running signal was observed in DCS - the motor was stopped from an RCU at field as it could not be stopped from DCS. This time the technician racked out the breaker and put into the test position and tested it all appeared to be ok. He then racked in into service and the motor was started - it ran for half a minute and flashover occurred and as a result the upstream protection tripped. The primary side of the transformer has two cables of 3 core 185sqm terminated on it. One cable sustained some burning. The transformer had some oil leakage at the relief pressure valve.
The cable was tested IR at 5000V DC and the reading are 400GOHMS. The transformer was tested and the IR value is 2.9G OHMS. Al tests necessary wire carried and transformer is declared ok - oil tests- DGA, BD, RATIO, CORE TEST THE WHOLE LOT. The question what could have caused such a flashover on CB? Is there any body who can help
The motor was started but no running signal was observed in DCS - the motor was stopped from an RCU at field as it could not be stopped from DCS. This time the technician racked out the breaker and put into the test position and tested it all appeared to be ok. He then racked in into service and the motor was started - it ran for half a minute and flashover occurred and as a result the upstream protection tripped. The primary side of the transformer has two cables of 3 core 185sqm terminated on it. One cable sustained some burning. The transformer had some oil leakage at the relief pressure valve.
The cable was tested IR at 5000V DC and the reading are 400GOHMS. The transformer was tested and the IR value is 2.9G OHMS. Al tests necessary wire carried and transformer is declared ok - oil tests- DGA, BD, RATIO, CORE TEST THE WHOLE LOT. The question what could have caused such a flashover on CB? Is there any body who can help