Hey guys,
Hope you all are doing great!
A tech observed a strange phenomenon yesterday. He said that he had two 100KW,415V,50Hz gas generators with identical ratings, parameters and components. Both managed by Deepsea 8610 controllers. When he tried to sync them both, they synced perfectly on no load. But as soon as he applied a load, even as small as 5kW(through a load bank), they both started to behave oddly i.e. their currents will shoot as high as 250A and it seemed like one generator is taking the other as load and then the other takes the first as load and this loop is cyclic. Then they both trip.
Anyone with similar experience? Any ideas?
Regards,
Mutahir
Hope you all are doing great!
A tech observed a strange phenomenon yesterday. He said that he had two 100KW,415V,50Hz gas generators with identical ratings, parameters and components. Both managed by Deepsea 8610 controllers. When he tried to sync them both, they synced perfectly on no load. But as soon as he applied a load, even as small as 5kW(through a load bank), they both started to behave oddly i.e. their currents will shoot as high as 250A and it seemed like one generator is taking the other as load and then the other takes the first as load and this loop is cyclic. Then they both trip.