Recently we have faced a unit trip while Auto Changeover got initiated by Coalescing filter Condensate level switch malfunction.
This is a Frame 9E unit running with Mark Vie Control system in TMR configuration.
Before unit trip, it was running on Base load and with Fuel Gas. We have low BTU gas with BTU value of 470 BTU/SCF.
During investigation it has been observed that Unit load increased during fuel change over and caused shifting of Temperature control from CPD to FSR temperature and eventually unit tripped on high exhaust temperature.
Following indications appeared before trip:
1-FSR Temperature Reference Active
2-Exhaust Temperature High
3-Exhaust Overtemperature Trip
I believe FSR should have been reduced and control system should have limited the load which did not happen in this case.
Kindly provide your suggestions/analysis for the event. I am attaching the events summary and log for reference.