D
We have Frame-6 GT M-IV controlled. Our <R>,<S>,<T>, IGV opening feedbacks are 71%, 83%,85% resp. In field local position shows 71%. Because of S & T processor final IGV feedback is 83% i.e full open condition. As a result we there is GT load limitation. We get only 22 MW against rated 30 MW. Can the problem be solved in GT running condition or Shutdown is must?