Gateway between Honeywell PLC and GE-Fanuc 90-70
R
Rajesh Kenge
I am trying to connect a honeywell PLC and GE Fanuc 90-70 PLC on a Ethernet. Can anybody suggest me a gateway between the 2 makes. I want to transfer data from Honeywell PLC and GE-Fanuc PLC via a network Link. Is it possible??
Awaiting for responses
rajesh 13/6/2001
R
Raymond van der Tas
You could use the following components:
- OPC Server for Honeywell
- OPC Server for GE
- ICONICS DataWorX32 OPC Gateway
DataWorX32 is a software component which allows you to create the OPC links between the source and destination OPC Item (tags).
In case the source and destination OPC Servers reside accross a multidomain intranet/internet you will need to get DataWorX32 version 6.1 to make the links work.
For more information please contact iconics.com.
ICONICS EUROPE
R
Richard Theron - FieldServer
Hi Rajesh
Would you be connecting from GE-EGD or GE-SNP to C-bus ?
I am not sure what protocols and connections you have available.
There could be a couple of options.
Richard Theron
Anything possible, time & money only limits! hah
SST has the "X-link" gateway product that can bridge between the 2 protocols. http://www.mysst.com/xlink/content.asp
Unless you have the ability to run the GE HCT SRTP Enet protocol on the Honey or communicate to each via an HMI of sorts acting as a "virtual bridge" to "map" the data over you have a dilema. Someone ( Honey or GE9070) has to initiate the comm channel and content packet i.e.; using commreqs in the 9070.
or EtherNet Global Data "EGD" if supported by the Honeywell.
What model PLC Honeywell??
Please advise and I'll give you a hand in checking out
[email protected]
Alfredo Quintero
Rajesh:
I do not know how to connect through Ethernet these two PLCs. However, I can propose Profibus. The SST's 5136-PFB-VME can sit in a GE 90-70, either standard 90-70 or the new PACSystem, and act as a Profibus DP slave. Another SST card, the SST-PFB-CLX works on the Honeywell PlantLogix system and Honeywell has a function block to configure the SST-PFB-CLX as a DP master. With this configuration the two CPUs can exchange 244 bytes both ways (that is 488 in total) at a very fast rate (12 Mbaud if the distance between the 2 is less than 100 metres.).