GE 9E/Non-DLN/Primary Fuel: GAS Low BTU/Start up and backup fuel: HSD, Control: Mark Iv
In CCPP
Plant was in commissioning phase, GT was operated only 300 hrs during these activities Combustion chamber 8 was burnt badly. Combustion chamber cover was melted near fuel nozzle area. fuel nozzle front flange and gas tip locking strips were melted. combustion liner cover cap and cowl was burnt. flow sleeve and chamber casing (can) were over heated.
After that fuel nozzle was pressure tested by GE but no internal leakage was found. design and material of parts were checked and found as per recommended.
These all parts were replaced, GT started again. after 5 days operation bore scope inspection was performed. Combustion line#8 was damage was started similar as previous.
Again investigation was done. this time little problem was observed at gas side. Condensate was coming with gas. It might be pass through coalscer filters. Gas composition was re checked, it was also varying from Design parameters.
It was recommended by GE to install knockout drums and increase gas temperature up to 70C, improve filtration.
All was done. lines were blow out, filters were replaced, additional heater installed, Knock out separator installed, C hangover from HSD to Gas was limit to 50%load after start up/during shutdown.
During each activity many check valves of water injection, fuel oil and purge air were found passing in reverse direction and as well as in forward direction before recommended pressure. Fuel oil mixing was found from water injection manifold, and fuel oil also in purge air manifold. These were also replace.
Moreover each possible relative system were checked and recommended action were taken.
And now after two week operation same failure happened at chamber-9. liner is worst damages well as fuel nozzle, combustion chamber cover and flow sleeve are also affected. Liner particles also travel forward to affecting transition piece.
In each accident parts of liner and cover also affect forward hot gas parts.
In each time all parameters were normal, our focus was at exhaust temperatures, in first case was absolutely normal. second time only once a single thermocouple was showing high temperatures but spread was not high even that point. third time also temperatures very normal.
Now my question is very simple
Why...?
It is very interesting...GE machine is suffering since one year, I would appreciate to look in detail.
I will provide as much detail as I can, Picture if anyone want to see I can mail
Thanks
In CCPP
Plant was in commissioning phase, GT was operated only 300 hrs during these activities Combustion chamber 8 was burnt badly. Combustion chamber cover was melted near fuel nozzle area. fuel nozzle front flange and gas tip locking strips were melted. combustion liner cover cap and cowl was burnt. flow sleeve and chamber casing (can) were over heated.
After that fuel nozzle was pressure tested by GE but no internal leakage was found. design and material of parts were checked and found as per recommended.
These all parts were replaced, GT started again. after 5 days operation bore scope inspection was performed. Combustion line#8 was damage was started similar as previous.
Again investigation was done. this time little problem was observed at gas side. Condensate was coming with gas. It might be pass through coalscer filters. Gas composition was re checked, it was also varying from Design parameters.
It was recommended by GE to install knockout drums and increase gas temperature up to 70C, improve filtration.
All was done. lines were blow out, filters were replaced, additional heater installed, Knock out separator installed, C hangover from HSD to Gas was limit to 50%load after start up/during shutdown.
During each activity many check valves of water injection, fuel oil and purge air were found passing in reverse direction and as well as in forward direction before recommended pressure. Fuel oil mixing was found from water injection manifold, and fuel oil also in purge air manifold. These were also replace.
Moreover each possible relative system were checked and recommended action were taken.
And now after two week operation same failure happened at chamber-9. liner is worst damages well as fuel nozzle, combustion chamber cover and flow sleeve are also affected. Liner particles also travel forward to affecting transition piece.
In each accident parts of liner and cover also affect forward hot gas parts.
In each time all parameters were normal, our focus was at exhaust temperatures, in first case was absolutely normal. second time only once a single thermocouple was showing high temperatures but spread was not high even that point. third time also temperatures very normal.
Now my question is very simple
Why...?
It is very interesting...GE machine is suffering since one year, I would appreciate to look in detail.
I will provide as much detail as I can, Picture if anyone want to see I can mail
Thanks