Hello all, looking for some assistance. Im trying to replace some old rosemount transmitters with updated ones and in this current case, its a externally powered not smart 0-5VDC, setup as TMR. After i hook up the new rosemount running hart 4-20ma, i can get a good reading in toolbox once downloading the new parameters to controller R. Once i update S, the readings go negative -33PSI on both, then once i update controller T, all 3 are -55psi (Should be 0PSI). Am i missing something obvious here or is this why it was originally a 0-5 setup and 4-20ma will not work in this case?
Thanks