GE MkIV Comm to Wonderware HMI

L

Thread Starter

Larry Couch

Does anyone know the pitfalls and/or impossibilities of communicating with a GE SPEEDTRONIC Mk IV panel through a Wonderware HMI package using MODBUS?
 
R

Richard Theron

Hi

We (FieldServer) have done the integration from Wonderware to Speedtronic MKIV successfully using our communication bridge, the communication bridge
is essentially a black box which we load different protocols into it, in this case GE Speedtronic MKIV and Modbus TCP/IP and the points are then mapped through from GE Speedtronic to Wonderware. This application worked well.

Regards

Richard
 
P

PAMBOS CHARALAMBOUS

We want to connect two MK4 speedtronic controllers with an RTU. The protocol must be Modbus RS485. Can you offer a solution for this problem?
 
Several companies ahve products that would suit your needs. Both CSE engineering and Control system technolgies have HMI products for the MK-4 that support modbus. I believe both have products that can support modbus directly to the panel.

PRISM systems has an OPC server that we are using for native data collection from MK-4 to wonderware historian - it is for use on the MK-4's that are on arcnet - it is only one-way though but well suited for a historian.
 
C

Craig Corzine

Pambos,

CSE Engineering, Inc. does have a gateway solution which communicates to the Mk IV in its native communication protocol and can provide full bi-directional communications in many protocol formats. IE: OPC, Modbus (Serial and TCP/IP), All FANUC protocols, All Allen-Bradley protocols, Siemens, Bailey, Westinghouse, etc.

If you wish further information please contact Svitlana Palona at +1 - 925-686-6733.

Regards,
Craig
 