B
We operate 2 units of Combustion Gas Generators GE-NP MS-5001-PA firing with Gasoil to supply electrical power for our Petrochemical complex. Total power requirement is 20 MW, our 2 CTGs both running in ISOCH mode, IGV control Auto ON with 10 MW load each CTG. When 1 CTG trip, the other CTG can load up till 18.4 MW within 0.95 second but the frequency drop to 48.05 HZ causing our plant Under frequency load shedding activated (UFS relay setting in 48.5Hz).
Do you any idea to speed up the ramping rate or to avoid the bus frequency drop below 48 Hz.
Thank you for your help to solve our problem.
Best regards,
Budi MP
[email protected]
Do you any idea to speed up the ramping rate or to avoid the bus frequency drop below 48 Hz.
Thank you for your help to solve our problem.
Best regards,
Budi MP
[email protected]