Ebi/abdi,
According to Mambo's and mhwest's explanations, the problem could very well be the ignitor position. What they're describing is that the tip of one or both of the ignitors--if inserted too far into the combustion liner--gets VERY hot during diffusion flame operation in Primary and Lean-Lean combustion modes, hot enough to ignite fuel in the primary combustion zone once the air/fuel mixture gets above minimum combustion mixture (richens up enough to be capable of diffusion flame).
Once more, during a Lean-Lean to Premix transfer, the fuel to the primary combustion zone is completely shut off (it's all directed to the secondary combustion zone). Then, once flame is NOT detected for a few seconds, the gas control valve that directs fuel to the primary combustion zone starts opening to re-admit fuel to the primary combustion (as the fuel to the secondary combustion zone is reduced at the same rate--this to prevent load swings). IF there is some ignition source--the extremely hot tip of an ignitor that is inserted too far into the combustion line, for example--then the fuel that is being re-admitted to the primary combustion zone can be re-ignited. So, just as you describe some time after fuel starts being re-admitted into the primary combustion zone if there is something hot enough to ignite the fuel into a diffusion flame then, voila! Extended Lean-Lean combustion mode is switched to. (In fact, if flame is detected in the primary combustion zone during a Lean-Lean to Premix transfer or during Premix mode, the ignitors are ignited for a short period--just to ensure that ALL the primary combustion zones are ignited (through the cross-fire tubes) to prevent high exhaust temperature spreads from damaging the hot gas path turbine buckets.
When in Premix combustion mode, there is no diffusion flame in the primary combustion zone--even though approximately 80% of the fuel is being introduced into the primary combustion zone. To get the low temperatures required to reduce NOx emissions it's necessary to extinguish the flame in the primary combustion zone that exists during Primary and Lean-Lean operation-and the only way to do that is to remove all the fuel from the primary combustion zone.
Once the diffusion flame is out (because there is no fuel flowing into the primary combustion zone for a few seconds) then fuel starts being re-admitted to the primary combustion. Under normal circumstances there is no ignition source in the primary combustion zone and the air/fuel mixture is so lean that diffusion flame does not exist in the primary combustion zone. The premixing of the gas fuel in the primary combustion zone is sufficient to produce the hot gases required for the turbine to produce torque--but not so hot that excessive NOx is formed.
The most common source of primary combustion zone re-ignition in GE-design heavy duty gas turbine DLN-I combustion systems is the presence of hydrocarbon-based solids which are so hot they can ignite the natural gas fuel--once there is enough fuel to be ignited. Such solids come from liquid contaminants in the gas fuel that "coke" and form solids on the fuel nozzles (usually) that get VERY hot, hot enough to ignite gas fuel--once the air/fuel mixture reaches the minimum mixture--and cause the unit to transfer to Extended Lean-Lean mode. Such contaminants include lubricating oil (from the natural gas compressors), seal oil (from the natural gas compressors), diesel and gasoline (yes--both do mysteriously get into natural gas pipelines; gas analysis reports have confirmed this on many occasions), and other hydrocarbon-based liquids entrained in natural gas pipelines.
So, try to envision what's going on during a Lean-Lean to Premix transfer when fuel is shut off to the primary combustion zone then re-admitted, and recognize that any ignition source (such as a hot or glowing ember, or the over-heated tip of an improperly inserted ignitor) can cause the fuel to ignite into a diffusion flame when the air/fuel mixture gets high enough as fuel is being re-admitted to the primary combustion zone as the Lean-Lean to Premix transfer is being completed.
Were the ignitors replaced during the HGPI? Was the insertion depth set when the new ignitors were installed? (This usually requires a unique tool to measure the distance from the ignitor mounting flange to the inside edge of the combustion liner.) If the ignitors, or even just one of the two ignitors, were/was replaced and the insertion depth was not set correctly then this could indeed by the "sparking gun" in your problem.
Please write back to keep us informed of the progress and resolution.