On 27th February 2012 at around 08:30 AM the grid fed from gas turbine frame 5, 19.5 MW, 60 Hz, 11.5 KV was subjected to electrical surge due to ground fault on a high voltage motor winding. Some under voltages relays in few substations operated but the generator relays didn’t operate. The vibration on no.3 bearing generator side reached 0.66 in/s for few seconds and then dropped to 0.16 in/s while the machine was making 12 MW. After 23 hours the vibration start to go up to 0.22 in/s after 13 hours reached to 0.26 in/s with same load, after another 18 hours it reached to 0.36 in/s it took another 21 hours to reach 0.49 in/s. the vibration on the reduction load was excessive so that within 3 meters distance from gear box we could feel heavy vibration under our feet. the vibration on the gear inboard was measured and found to be 41.5 mm/s, while no.1&2 bearing reading were 0.07 in/s & 0.09 in/s. we have stopped the machine and when we open gear inspection window we found the high speed pinion 19 tooth out of 61 were broken (towards the generator) and the 2 bearing on low speed side were rubbed. We are suspecting the ground fault on the high voltage motor was the root cause of the gear failure. I appreciate your feed back if you come across similar incident.