We are running 2 frame 6 GT (Only gas) DLN-1 in synchronization with grid (Floating). Complex load demand 48MW Both GT's are kept in Droop/ Preselect mode. We have 4% droop. We have provided high & low frequency grid power isolation. Also we had provide a logic that on isolation of grid one machine will come on ISO mode as per selection. If that machine trips second machine will come o ISO mode.
We had one unresolved experience. Once the grid frequency had increased due to external disturbance. In spite of our machines in preselect mode the load on both machines reduce by 8 mW. On high frequency (50.4 h) the grid de-synchronized and we went to island operation mode . But the machine did not come on ISO mode as per defined logic .On under frequency both machine tripped since both were on droop only.
When we studied, L90LL for load lower command is coming which in turn actuate L70LX5 high temperature spread lower which prevented L83SCDT droop to ISO permissive. So machine did not come on ISO.
Two matters is mystery for us
Why this (L90LL) prevailed since machine was on lower load. Also why in spite of preselect mode our machines could not achieve the preselect value is un explainable.
De-synchronization occurred in 4 seconds, with in this time machine could not achieve the preselect set value. Trip sequence occurred in 3 minutes. Within this time machine could not come on ISO. After tripping of one machine second machine also could not come on ISO. Can someone throw some light on these from their experience.
We had one unresolved experience. Once the grid frequency had increased due to external disturbance. In spite of our machines in preselect mode the load on both machines reduce by 8 mW. On high frequency (50.4 h) the grid de-synchronized and we went to island operation mode . But the machine did not come on ISO mode as per defined logic .On under frequency both machine tripped since both were on droop only.
When we studied, L90LL for load lower command is coming which in turn actuate L70LX5 high temperature spread lower which prevented L83SCDT droop to ISO permissive. So machine did not come on ISO.
Two matters is mystery for us
Why this (L90LL) prevailed since machine was on lower load. Also why in spite of preselect mode our machines could not achieve the preselect value is un explainable.
De-synchronization occurred in 4 seconds, with in this time machine could not achieve the preselect set value. Trip sequence occurred in 3 minutes. Within this time machine could not come on ISO. After tripping of one machine second machine also could not come on ISO. Can someone throw some light on these from their experience.