Yes of course, its a hart. HART 4-20mA.Have you checked the model number and made sure that the transmitter is not Foundation Fieldbus, or Profibus, or Modbus output?
Try to have a look on the name tag attached.Have you checked the model number and made sure that the transmitter is not Foundation Fieldbus, or Profibus, or Modbus output?

Yes, that's the way I did.Is it wired:
24Vdc (+) to 2051 (+)
2051 (-) to resistor
resistor to 24Vdc (-)/common
Yes, because my trex has only two communication port, for Ff and Hart which are both unpowered thats why i had to use an external supplyAre you connected to the B connection (on the extreme right, as shown below) on the TREX for an externally powered loop?
View attachment 2915
3.6 Device connection wizard
If the Trex unit cannot automatically detect or connect to the device, tap HART or Fieldbus on the Connect - Select screen to start the device connection wizard. The wizard displays a set of questions to help you connect to the device. You may see one or more of the questions below depending on the setup of your device. The questions may appear in a different order than listed below.
• Do you intend to provide power from the Trex unit? (This is available only if the Device Communicator Plus communication module is attached to the Trex unit.)
• Is the Trex unit connected to a transmitter or a positioner?
• Do you want to change the polling options?
• Do you want to increase loop resistance? (This enables the internal resistors.)
• Do you want to increase loop current? (This is available for only positioners.)
In the Field Communicator application, the device connection wizard is the only way to enable the Trex unit to power a device, change the polling options for HART and fieldbus, enable the internal resistors within the Trex unit, or increase current to positioners.
If the device connection wizard completes its process and cannot connect to the device, a message is displayed. Tap Cancel to return to the Connect - Select screen to retry the connection process.
But thisAre you connected to the B connection (on the extreme right, as shown below) on the TREX for an externally powered loop?
View attachment 2915
Because the trex that I have is in the upper part of the attached photo.Interesting that nothing in the TREX spec sheet mentions lack of ability of the TREX to power the loop; in fact, there are multiple references to the advantages of the TREX being able to power the loop to configure a HART device before the electrical infrastructure is in place in greenfield builds. No mention in the manual either.
Other than checking the resistor with a Ohmmeter to make sure it's 250 -500 Ohms, I'm out of ideas. Maybe it's time to call Emerson and ask why the TREX won't connect.