Report from the field:
A flow meter with a Modbus RTU RS-485 port runs OK when polled by a Windows box with a USB/485 converter.
But when the Modbus master is replaced with either 1 of 2 PLCs, the Modbus comms runs only 3-5 minutes, before it fails. While running, comms passes valid data.
It doesn't matter if local VFD's are running or turned off, the result is the same.
The cabling was tested with a slave PLC replacing the flow meter and data was passed successfully beyond the 5 minute mark.
This is low speed, 9600 baud, operation.
The installed claims there is shielded twisted pair cabling. I'm getting confirmation on whether there's a signal ground connection on the PLC serial port (there is on the flow meter).
Presence or absence of 120 Ohm terminating resistors do not make a difference.
In one test, a PLC was placed within a meter of the flow meter and comm ran for 4 minutes then died.
I'm stuck. Any ideas?
A flow meter with a Modbus RTU RS-485 port runs OK when polled by a Windows box with a USB/485 converter.
But when the Modbus master is replaced with either 1 of 2 PLCs, the Modbus comms runs only 3-5 minutes, before it fails. While running, comms passes valid data.
It doesn't matter if local VFD's are running or turned off, the result is the same.
The cabling was tested with a slave PLC replacing the flow meter and data was passed successfully beyond the 5 minute mark.
This is low speed, 9600 baud, operation.
The installed claims there is shielded twisted pair cabling. I'm getting confirmation on whether there's a signal ground connection on the PLC serial port (there is on the flow meter).
Presence or absence of 120 Ohm terminating resistors do not make a difference.
In one test, a PLC was placed within a meter of the flow meter and comm ran for 4 minutes then died.
I'm stuck. Any ideas?