Unit runs on Gas with Primary and Secondary Fuel Nozzles. Exhaust Spread was 27C after MI in March 2009. Problem started in July 2010. Chronology of the problem as follows:
Mar 2009: Turbine Major Inspection performed
Apr 2009: Exhaust Spread was 27C
01/30/10: 3 Exhaust Trips Signals reached limits
02/01/10: Exh T/C H & K looped. Spread normal.
07/02/10: Plant tripped on high exhaust spread
07/11/10: Sludge noticed in Fuel Gas Pig Tails
07/11/10: FG lines cleaned & FN Tips replaced
08/17/10: Unit started. Spread still abnormal.
July/Aug’10: Low & High Reading T/C looped
08/31/10: Spread 58C with 2L & 2H T/C rejected.
09/4-18/10: Spread rise from <80C to 97C
09/19-29/10: Spread rise from 100C to 105C
10/1-6/10: Spread remains high at 98C to 100C
Exhaust T/C Readings in "C" on 10/19/2010 as follows:
T/C 21TE450A:522C
T/C 21TE450B:513
T/C 21TE450C:502
T/C 21TE450D:499
T/C 21TE450E:485
T/C 21TE450F:484
T/C 21TE450G:491
T/C 21TE450H:492
T/C 21TE450I:450
T/C 21TE450J:429
T/C 21TE450K:476
T/C 21TE450L:463
T/C 21TE450M:508
TTXM:488
TTXSPL:63
TTXSP1:93
Low Limit:449
High Limit:521
Gas Turbine drives Syn Gas Compressor in Ammonia Plant that is critical for Plant running. The Controls team have confirmed that all the 13 exhaust T/C are normal and readings are real. It is quite obvious that it is not only a real but an excessive combustion trouble. Plant operation is vital and hence all probable causes needs to be identified for giving a clear action plan to shutdown the unit. Some of them have tried to list down.
Fuel Nozzle
-Clogging of nozzle
-Effective area flow not within limits
-Nozzle not calibrated to the specified limits
-Incorrect nozzle internals
Combustion Air
-Hot air leak from Cross Fire Tubes
-Excess air leaking into WI piping
-Fouled compressor
Fuel Gas
-Gas leak from Pig Tails
-Contamination of gas upstream
Combustion
-Huls spring seal fit improper
Transition Piece Assembly
-Missing TP end seals
Request:
1) Please advise additional probable causes.
2) Is HGPI advisable? to inspect the Stage Nozzles, Buckets & Shrouds, for the reason that unit had been running on high exhaust spread since July'10 until now.
Please let me know any further information needed.
Mar 2009: Turbine Major Inspection performed
Apr 2009: Exhaust Spread was 27C
01/30/10: 3 Exhaust Trips Signals reached limits
02/01/10: Exh T/C H & K looped. Spread normal.
07/02/10: Plant tripped on high exhaust spread
07/11/10: Sludge noticed in Fuel Gas Pig Tails
07/11/10: FG lines cleaned & FN Tips replaced
08/17/10: Unit started. Spread still abnormal.
July/Aug’10: Low & High Reading T/C looped
08/31/10: Spread 58C with 2L & 2H T/C rejected.
09/4-18/10: Spread rise from <80C to 97C
09/19-29/10: Spread rise from 100C to 105C
10/1-6/10: Spread remains high at 98C to 100C
Exhaust T/C Readings in "C" on 10/19/2010 as follows:
T/C 21TE450A:522C
T/C 21TE450B:513
T/C 21TE450C:502
T/C 21TE450D:499
T/C 21TE450E:485
T/C 21TE450F:484
T/C 21TE450G:491
T/C 21TE450H:492
T/C 21TE450I:450
T/C 21TE450J:429
T/C 21TE450K:476
T/C 21TE450L:463
T/C 21TE450M:508
TTXM:488
TTXSPL:63
TTXSP1:93
Low Limit:449
High Limit:521
Gas Turbine drives Syn Gas Compressor in Ammonia Plant that is critical for Plant running. The Controls team have confirmed that all the 13 exhaust T/C are normal and readings are real. It is quite obvious that it is not only a real but an excessive combustion trouble. Plant operation is vital and hence all probable causes needs to be identified for giving a clear action plan to shutdown the unit. Some of them have tried to list down.
Fuel Nozzle
-Clogging of nozzle
-Effective area flow not within limits
-Nozzle not calibrated to the specified limits
-Incorrect nozzle internals
Combustion Air
-Hot air leak from Cross Fire Tubes
-Excess air leaking into WI piping
-Fouled compressor
Fuel Gas
-Gas leak from Pig Tails
-Contamination of gas upstream
Combustion
-Huls spring seal fit improper
Transition Piece Assembly
-Missing TP end seals
Request:
1) Please advise additional probable causes.
2) Is HGPI advisable? to inspect the Stage Nozzles, Buckets & Shrouds, for the reason that unit had been running on high exhaust spread since July'10 until now.
Please let me know any further information needed.