Hi,Take a look at this:
https://product-help.schneider-electric.com/PowerLogic-PM8000/en-us/content/03-communications/configuring-custom-modbus-data-using-ion-setup.htm?TocPath=Communications|Modbus|_____8
And this:
It seems that if you selected "Default" in the Modbus Slave Mode Setup, the register mapping may not be editable. It appears you would instead need to select "Modified" in the Modbus Slave Mode Setup to be able to add additional mappings to the default Modbus map.
Hi,please contact the company where you bought the equipment/software from.
Thank you for the input.Most Modbus slave/servers that are field devices do not have editable slave maps. PLCs, PACs, DCSs, wireless gateways are more likely to have an editable slave/server map.
Is this what you're looking for?Is there other way to activate or enable the digital input in ion 7550 so that it can be linked to the Vista for circuit breaker status?
Hi,Is this what you're looking for?
https://www.se.com/in/en/faqs/FA210264/