Helllo,you can ask the resident engineer to see what is the problem in this case.I would suggest you to se the functional description document to understand what is going to better see the implications.Also are you trying to start up the gas turbine in droop or isochronous,because,unless a software is implemented.You should be starting the other turbine in droop mode anyway,I think that might be the problem,but anyway I suggest you to see the functional descriptionHi all,
I have been encountering some issues that relatable to this thread, and wondering if someone can help educate me in this matter.
First of all I am new (just started working in powerplant for a paper making factory)
We have 2 units of GE 6F rated at 80MW each, with Mark IVe control system. Our powerplant is just supplying the power only for our own factory ( island) and didnt have national grid connection. The maximum factory uses load as of now is around 65MW.
We only running one unit of GT at one time (enough to support the load) running at Isochronous speed control.
Also in Island mode ON.
The problem that we encountered is when we started the other one GT and after synchronised, with intended to run at preselect mode, the newly started GT couldn’t loading the load ( just merely 1MW) it cannot raise the load as per preselected value at 6MW.
Why is this happening, is there anything that we missed, such as turning off the island mode for the new GT or manually raising the excitation ,etc .
Is there anything we as the operator can do, hoping someone can helps me out to understand this better.
Big thanks