We have MS6001 dual fuel Gas Turbine for Generator drive controlled by original Mark V TMR.
Strange phenomena occurred in successive 3 days (GT running in Gas Fuel)
#1. Day 1 : There is Trip Alarm L71GHH1 <QD1> ("gas scrubber liquid level High Trip"),But the unit still running normally. This contact logic is one of input trip for L4PSTX2 .
#2. Day 2 : Unit is trip without any trip alarm. In the Trip log data shows that L4 is drop by it self even L4T & L94T still in "false/0"
Trip Log ,Time ; L4 ; L4T ; L94T
10:15:29 ; 1 ; 0 ;0
10:15:30 ; 0 ; 0 ;0
10:15:31 ; 0 ; 0 ;0
#3. Day 3 : Unit is trip without any trip alarm. In the trip log data shows that L4 is dropped by : L4T <-- L4PST <-- L4PSTX2.
Trip Log ,Time ; L4 ; L4T ; L4PST ; L4PSTX2
07:51:01.00; 1 ; 0 ; 0; 1
07:51:02.00; 0 ; 1 ; 1; 0
07:51:03.00; 0 ; 0 ; 0; 1.
R,S,T, C condition after trip in A7 state, & no diagnostic alarm at trip timing.
Check to all trip input logic cross reference to alarm.dat , all trip input have its own Alarm ID.
The only action that we've done is change 71GHH1 Switch due to intermittent open of contact & Reboot all computer R,S,T,C due to strange phenomena #1,#2,#3
Test trip was done to check 71GHH1 ==> Unit was trip & Alarm as #1 appear("gas scrubber liquid level High Trip")& trip logic data is same as#3.
Appreciate for any opinion of possible cause for this problem.
Strange phenomena occurred in successive 3 days (GT running in Gas Fuel)
#1. Day 1 : There is Trip Alarm L71GHH1 <QD1> ("gas scrubber liquid level High Trip"),But the unit still running normally. This contact logic is one of input trip for L4PSTX2 .
#2. Day 2 : Unit is trip without any trip alarm. In the Trip log data shows that L4 is drop by it self even L4T & L94T still in "false/0"
Trip Log ,Time ; L4 ; L4T ; L94T
10:15:29 ; 1 ; 0 ;0
10:15:30 ; 0 ; 0 ;0
10:15:31 ; 0 ; 0 ;0
#3. Day 3 : Unit is trip without any trip alarm. In the trip log data shows that L4 is dropped by : L4T <-- L4PST <-- L4PSTX2.
Trip Log ,Time ; L4 ; L4T ; L4PST ; L4PSTX2
07:51:01.00; 1 ; 0 ; 0; 1
07:51:02.00; 0 ; 1 ; 1; 0
07:51:03.00; 0 ; 0 ; 0; 1.
R,S,T, C condition after trip in A7 state, & no diagnostic alarm at trip timing.
Check to all trip input logic cross reference to alarm.dat , all trip input have its own Alarm ID.
The only action that we've done is change 71GHH1 Switch due to intermittent open of contact & Reboot all computer R,S,T,C due to strange phenomena #1,#2,#3
Test trip was done to check 71GHH1 ==> Unit was trip & Alarm as #1 appear("gas scrubber liquid level High Trip")& trip logic data is same as#3.
Appreciate for any opinion of possible cause for this problem.