Which one better? Using DDR or Capture Block?Mark VI or Mark VIe?
for Mark VI. There are 2 places to archive Trip logs in the Controller. Either using the Dynamic Data Recorder (DDR) or capture buffer blocks.
For the DDR:
- Open up your GT M6b file. Verify there are some DDRs are configured in the controller.
- On the left side, there is a sub menu called "Dynamic Data Recorder". Check to see if it has DDR1, DDR2, DDR3, etc configured within this sub menu. If not, move on to Capture blocks
For the Capture blocks:
- Open up your GT M6B file. This is written in the code. Usually, it is under Functions then a program called "Trip_Log". Within that program, a few 'Capture' blocks should be configured with a bunch of points.
You can then view your DDR or captured blocks using the Trender. Or if you have a historian configured (.thb file), then that will automatically download the trip log files.
For Mark VIe:
- open the GT file in the TCW. Go to the Dynamic Data Recorder tab.
- Make sure DDRs are configured with points
- open up your GT workstation. Go to the 'Recorder' tab. If one is not configured, then this workstation is not configured to automatically DL the DDR.
- Under the recorder tab, it will show you were those files are automatically uploaded from the controller. Usually this is C:\RecorderData.
You can also use TrenderST to view DDR.
| Thread starter | Similar threads | Forum | Replies | Date |
|---|---|---|---|---|
| M | over temp trip in frame 6 mark 5 gas turbine | Power Generation | 9 | |
| N | GE Gas Turbine Mark VIeS - Auto Purge Trip | Process Control | 1 | |
| M | Mark VIe tracing out the trip trigger | Power Generation | 6 | |
| U | Mark vi Trip History collection | Power Generation | 0 | |
| S | MARK-VI TRIP HISTORY | Power Generation | 2 |