Good day to the control.com community,
I am asking for some education on MKVI generator synchronization. We operate 2 GE 7EA MKVI TMR EX2000 gas turbines, circa 2005, baseload operations. We came offline this past weekend for an offline wash and replacement of a failed VSVO card. We encountered trouble trying to sync after our short outage. We have had problems similar to this twice in the past on both units, but never fully figured out the cause.
Typically when we reach FSNL we engage autosync and the unit will sync within 1 revolution of the sync scope, voltage and speed are steady. We have never used manual sync. We have no aux relays inline with the generator close coil, we let the MKVI control of K25P, K25A and K25 govern sync.
This past weekend the unit reached FSNL and was ready to sync, there were no diagnostic alarms on the MKVI. The operator selected auto sync, but the unit did not close the breaker. We started a trend and were able to verify that the MKVI was trying to close the breaker by energizing the K25 relay. Investigation showed that we had failed to properly rack in the breaker, the unit was kept at FSNL and the breaker condition was resolved. The VTUR card set a diagnostic for “breaker slower than adjustment limit allows”, which I expected.
Following this, several attempts to sync were unsuccessful, several different diagnostics were set and sync lockout alarms were generated. Alarm from the VTUR, GEN_SYNC_Lo would set, causing the “sync lockout”. As well, 2 to 3 VPRO cores would set diagnostic fault 90, indicating trouble with the K25A relay. Reading the Speedtronic system guide GEH-6421 chapter 7, Applications, it indicates that GEN_SYNC_LO will set if the K25 contacts are closed when they should not be, OR the K25A is not picked up before K25. Although the alarm in the MKVI says this alarm is generated by “K25 relay contacts stuck closed or welded”.
This same unit had this same problem almost 2 years back. While a GE TA was en route to diagnose the problem he suggested replacing the TTUR card. The unit was shut down, card replaced and the unit restarted and synced without any trouble, as I am told. Whether the card fixed it or it was just coincidence I can’t say.
This weekend, due to the faults stored, we replaced all 3 relays on the TTUR card. The next sync attempt was successful, although a single VPRO core stored the diagnostic fault 90. I still believe that the only reason the unit synced was that 2-3 VPROs did not set a diagnostic as they did on the previous attempts, and that there is still something going on with the timing of the K25 relay group. Our second unit has set this same diagnostic at times when syncing but again usually only 1 core. I did find that quite a few signals from the TTUR that indicate the command and feedback status of the K25 K25A and K25P relays are “not used” so I can’t trend them. I will fix this at our next outage.
I am curious if CSA or another group member might have been down this road before, the archive did not provide any of the in depth answers I want. I did compare card settings to some .m6b files I have from some other 7EAs and the voltage and slip settings are the same, 10 deg slip, etc.
I thank any and all in advance for their time and comments. I would like to make sure I fully understand this system, so I can be better prepared for my next battle.
I am asking for some education on MKVI generator synchronization. We operate 2 GE 7EA MKVI TMR EX2000 gas turbines, circa 2005, baseload operations. We came offline this past weekend for an offline wash and replacement of a failed VSVO card. We encountered trouble trying to sync after our short outage. We have had problems similar to this twice in the past on both units, but never fully figured out the cause.
Typically when we reach FSNL we engage autosync and the unit will sync within 1 revolution of the sync scope, voltage and speed are steady. We have never used manual sync. We have no aux relays inline with the generator close coil, we let the MKVI control of K25P, K25A and K25 govern sync.
This past weekend the unit reached FSNL and was ready to sync, there were no diagnostic alarms on the MKVI. The operator selected auto sync, but the unit did not close the breaker. We started a trend and were able to verify that the MKVI was trying to close the breaker by energizing the K25 relay. Investigation showed that we had failed to properly rack in the breaker, the unit was kept at FSNL and the breaker condition was resolved. The VTUR card set a diagnostic for “breaker slower than adjustment limit allows”, which I expected.
Following this, several attempts to sync were unsuccessful, several different diagnostics were set and sync lockout alarms were generated. Alarm from the VTUR, GEN_SYNC_Lo would set, causing the “sync lockout”. As well, 2 to 3 VPRO cores would set diagnostic fault 90, indicating trouble with the K25A relay. Reading the Speedtronic system guide GEH-6421 chapter 7, Applications, it indicates that GEN_SYNC_LO will set if the K25 contacts are closed when they should not be, OR the K25A is not picked up before K25. Although the alarm in the MKVI says this alarm is generated by “K25 relay contacts stuck closed or welded”.
This same unit had this same problem almost 2 years back. While a GE TA was en route to diagnose the problem he suggested replacing the TTUR card. The unit was shut down, card replaced and the unit restarted and synced without any trouble, as I am told. Whether the card fixed it or it was just coincidence I can’t say.
This weekend, due to the faults stored, we replaced all 3 relays on the TTUR card. The next sync attempt was successful, although a single VPRO core stored the diagnostic fault 90. I still believe that the only reason the unit synced was that 2-3 VPROs did not set a diagnostic as they did on the previous attempts, and that there is still something going on with the timing of the K25 relay group. Our second unit has set this same diagnostic at times when syncing but again usually only 1 core. I did find that quite a few signals from the TTUR that indicate the command and feedback status of the K25 K25A and K25P relays are “not used” so I can’t trend them. I will fix this at our next outage.
I am curious if CSA or another group member might have been down this road before, the archive did not provide any of the in depth answers I want. I did compare card settings to some .m6b files I have from some other 7EAs and the voltage and slip settings are the same, 10 deg slip, etc.
I thank any and all in advance for their time and comments. I would like to make sure I fully understand this system, so I can be better prepared for my next battle.