Enough already with the beating up on the PLC scantime nonsense. I have, in the past 25 years used quite a few PLCs, and have resisted using the cheaper PLCs that you make frequent reference to. Use a decent PLC and you get predictable scan times. With PLC-5s I have controlled entire rail-car positioning and dumping systems with 12 ms scan time, bin sorters with 8 ms, positioners with 10 ms and 2 ms STI (I tested that one with solid operation on an STI of 1 ms). Those are scope tested, repetitive stable times. With the ControlLogic platform I'm doing large scale pump stations with flow computing, batching, sampling, first out alarm capturing, local HMI and SCADA interfacing all in 7 ms. So I don't see where the problem is. Every bit of "erratic" or "intermittant" problem I have been able to trace out with just decent logic approach to troubleshooting to someones (or my own) bad programming. The scan nature of the PLC is an attribute - not a problem. And the best part is, there are no secrets in PLC programming (that is until just recently with their silly program protection - and you can kill me if I ever use it). In the PLCs that I use there is nothing loose or erratic. In the end I'm with you though, I want to provide a magnitude better than what end users expect. That's whay I use PLCs.