Thanks A lot you cleared all my confusions ..best explanation everThis applies to ISLAND mode ("small" AC power generation and distribution system).
Ideally there should be one machine (prime mover and generator) operating in Isochronous Speed Control mode and that machine "absorbs" any changes in the load (loadS, actually--the sum of all the lights and motors and tea kettles and televisions and air conditioners and computers and computer monitors, etc.). The Isochronous machine will automatically adjust its load as the load changes (real power) up to the maximum rated load of the prime mover and down to zero watts/kW/MW of the prime mover. (More on that later.)
The other machines should all be in Droop Speed Control mode--that is the operating mode that allows a prime mover and its generator (or prime movers and their generators) to share load with other machines and with the Isochronous machine. Droop Speed Control is straight proportional control--there is nothing in the control system of the prime mover (the prime mover governor) that makes automatic adjustments to return the frequency of the generator to nominal (rated grid frequency) when it drifts above or below nominal. THAT'S the responsibility of the Isochronous machine (the machine with its prime mover operating in Isochronous Speed Control mode).
Let's have an example. A small system operating stably at this instant in time at 25 MW. There are five generators, each rated at 15 MW (the rating of the prime mover; the generator nameplate rating is slightly higher for each machine). One machine's prime mover governor is operating in Isochronous Speed Control Mode at 5 MW. The other four machine's prime mover governors are operating in Droop Speed Control Mode at 5 MW. So, five machine operating at 5 MW each, and the total load on the system is 25 MW. The system frequency is 49.97 Hz--which is pretty good, actually.
Somewhere on the system a large water pump motor is started; it's rated at 1.5 MW. The immediate effect of this motor starting is the system frequency will start to decrease. However, the Isochronous machine immediately senses the decrease in grid frequency (as do the Droop Speed machines) and the Isochronous machine immediately increases the energy flow-rate into the prime mover restoring its generator's (and the system's) frequency to approximately 50 Hz (50.04 Hz--pretty good, still!). The Isochronous machine's generator load increased to 6.5 MW. The other machines, operating in Droop Speed Control, had their frequendies change slightly when the motor started but they all (including the Isochronous machine) went to 50.04 Hz when the system stabilized (which it did very quickly), but their loads remained unchanged at 5 MW each. That's what's supposed to happen and it did so without ANY human operator intervention.
Now, let's say that was early in the morning and as the day progressed the load on the system slowly increased to nearly 44 MW. The Isochronous machine's load increased AUTOMATICALLY to 24 MW and the four Droop machines remained at 5 MW each with no change in electrical output. The system frequency is at approximately 49.91 Hz (still reasonably good)--being maintained automatically by the Isoch machine.
BUT, there's a chance the system load could continue to increase. And that means that the maximum power output of the Isoch machine's prime mover governor could exceed 25 MW. So, the WELL-TRAINED operator, under the guidance of the EXPERIENCED operations supervisor, decides to reduce the load on the Isoch machine. And, to do this the operator goes to one of the Droop machines and increases it's power output to 10 MW. The effect on the system as the load on this Droop machine is being increased is to increase the frequency of system (ALL the generators--including the Isoch machine's generator). BUT the Isoch machines prime mover governor AUTOMATICALLY reduces the load on the Isoch machine by the amount the load was increased on the Droop machine: 5 MW. And the system frequency (and that of all the generators synchronized to the system) was stable at about 50.07 Hz. The load on the Isoch machine is down to 19 MW, the load on one of the Droop machines is up to 10 MW, and the load on the remaining three Droop machines is unchanged at 5 MW--for a total of 44 MW.
I gotta stop here because Control.com has a maximum limit on the number of characters, and if I haven't exceeded the limit yet, I gotta be close.
TO BE CONTINUED.
Thank you for your response ,>>>!!CORRECTION!!<<<
I was able to correct an addition error (I should write the numbers down and add them--not try to do them in my head...) in my original post (Post #1). I have since spotted another error--a pretty big one, and it's too late for me to edit the post. I should have said the Isoch machine prime mover in the example was rated for 25 MW--not 15 MW. So the total of the capacity of the five generators in the example is (25+15+15+15+15) 85 MW. It's just an example, and it might be that some part of the loads supplied by the islanded system might be shutdown for plant maintenance, but for some reason the other machines were still running (possibly supplying steam to steam loads, for example). I intended to point to the Isoch machine as having a slightly larger capacity than the other machines (something that is common on smaller islanded systems). I then said the load on the Isoch machine increased to 24 MW during the day and could increase still further and exceed the 25 MW rating of the Isoch machine's prime mover.
I apologize for any confusion.
Thanks a lot for explaining it properly..... The part about new managers thinking “this time we’ll make isochronous load sharing work” and then discovering why everyone before them said don’t touch it was both painful and hilarious. Basically, two generators in pure isochronous without proper coordination is a great way to turn confidence into a blackout@afaq,
When a generator's prime mover governor operates in Isochronous Speed Control mode it wants to control the speed of the prime move and generator VERY tightly (for GE-design heavy duty gas turbines that's usually from 59.83 Hz to 60.17 Hz, or from 49.83 Hz to 50.17 Hz (so in the range of +/-0.17 Hz)--and when it senses any change in machine speed (which directly proportional to generator frequency) it acts VERY quickly to bring the machine speed back to nominal (50.0 Hz or 60.0 Hz).
If two generators and their prime movers are both operating in Isochronous Speed Control mode and are synchronized together BOTH m prime mover governors will respond to any change in machine speed (generator frequency) VERY QUICKLY! So, let's say the machine speeds (of the two machines since they are SYNCHRONIZED together and both operate exactly the same frequency!) dropped below 99.66%. BOTH machine prime movers will VERY QUICKLY try to increase the machine speeds (generator frequencies) and what will likely happen is that the system frequency will rise above 100.33% speed. Then both machines will then try simultaneously to decrease machine speeds (generator frequencies) and this leads to some very ROUGH and turbulent power generation which causes severe frequency deviations and usually will result in some system protective relay tripping one or both machines on over- or under-frequency.
There's really very little, or in some cases, no "gently ramping up" or down of fuel by a machine operating in Isochronous Speed Control mode. System frequency is just about the most important aspect of AC power systems. So, governors are designed to respond quickly to even slight deviations, and two machines with no "coordination" between then other than they sense the same speed changes (frequency changes) try to respond simultaneously things can get pretty ugly very quickly.
AC power generation systems were never designed to have more than one machine (generator prime mover) operating in "pure" Isochronous Speed Control mode at the same time while synchronized to the same grid. Yes, there are perversions of Isochronous Speed Control, usually called something like 'Isochronous Load Sharing' or 'Load Sharing' or something like that--but they require extra sensing systems for the machines to know what the other machine is producing and there's where the difficulty comes in because many system programmers really don't understand AC power generation fundamentals and these systems rarely perform well and quite often get abandoned in place (never used and never enabled). UNTIL some manager thinks HE knows how the system should operate and decides to start some testing without knowing how much training and experience the machine operators have to be prepared for what might happen and what to do in the (likely) event things go awry during this test. And once the test is over, it's usually decided NOT to try that again (enabling Isochronous Load Sharing without understanding how it works and what can happen and how operators should respond to system disturbances). Until the next new manager decides HE knows how to make the system work.... And the cycle repeats itself.
This--operating to generators in Isochronous Speed Control Mode--is just one of those things that one should be accepting of the admonition (advice) to never try it. Possibly with some "proven" Isochronous Load Sharing system in place, but "proven" almost never happens in reality because during testing of the Isochronous Load Sharing system usually the plant ends up going black (meaning the lights in the plant--and the surrounding facility/area--also go black) which means SOMEBODY has got some very serious EXPLAINING to do. And that doesn't happen more than once, usually. Owners and Plant Manages and Operations Supervisors are VERY sensitive to not having to make those explanations (because many don't really understand AC power generation fundamentals well enough to explain them to others after a blackout happens--because the only real "explanation" people asking for want (DEMAND) is that it won't happen again!!! (Which means no more testing or tuning, which means the system doesn't get properly configured and adjusted and tested to prove it works as intended.)
"Just don't do it," is very good, sound advice for your career when it comes to trying to operate two generators and their prime movers simultaneously in Isochronous Speed Control mode while synchronized together on the same grid. If there are analog meters in the Control Room when someone tries this they usually jump furiously from left to right and back and forth--until the lights go out. And, depending on the situation and circumstances such a result (a blackout) can be very career limiting.
@WTF? thank you for such an insightful explanation on the principles "governingThis applies to ISLAND mode ("small" AC power generation and distribution system).
Ideally there should be one machine (prime mover and generator) operating in Isochronous Speed Control mode and that machine "absorbs" any changes in the load (loadS, actually--the sum of all the lights and motors and tea kettles and televisions and air conditioners and computers and computer monitors, etc.). The Isochronous machine will automatically adjust its load as the load changes (real power) up to the maximum rated load of the prime mover and down to zero watts/kW/MW of the prime mover. (More on that later.)
The other machines should all be in Droop Speed Control mode--that is the operating mode that allows a prime mover and its generator (or prime movers and their generators) to share load with other machines and with the Isochronous machine. Droop Speed Control is straight proportional control--there is nothing in the control system of the prime mover (the prime mover governor) that makes automatic adjustments to return the frequency of the generator to nominal (rated grid frequency) when it drifts above or below nominal. THAT'S the responsibility of the Isochronous machine (the machine with its prime mover operating in Isochronous Speed Control mode).
Let's have an example. A small system operating stably at this instant in time at 25 MW. There are five generators, each rated at 15 MW (the rating of the prime mover; the generator nameplate rating is slightly higher for each machine). One machine's prime mover governor is operating in Isochronous Speed Control Mode at 5 MW. The other four machine's prime mover governors are operating in Droop Speed Control Mode at 5 MW. So, five machine operating at 5 MW each, and the total load on the system is 25 MW. The system frequency is 49.97 Hz--which is pretty good, actually.
Somewhere on the system a large water pump motor is started; it's rated at 1.5 MW. The immediate effect of this motor starting is the system frequency will start to decrease. However, the Isochronous machine immediately senses the decrease in grid frequency (as do the Droop Speed machines) and the Isochronous machine immediately increases the energy flow-rate into the prime mover restoring its generator's (and the system's) frequency to approximately 50 Hz (50.04 Hz--pretty good, still!). The Isochronous machine's generator load increased to 6.5 MW. The other machines, operating in Droop Speed Control, had their frequendies change slightly when the motor started but they all (including the Isochronous machine) went to 50.04 Hz when the system stabilized (which it did very quickly), but their loads remained unchanged at 5 MW each. That's what's supposed to happen and it did so without ANY human operator intervention.
Now, let's say that was early in the morning and as the day progressed the load on the system slowly increased to nearly 44 MW. The Isochronous machine's load increased AUTOMATICALLY to 24 MW and the four Droop machines remained at 5 MW each with no change in electrical output. The system frequency is at approximately 49.91 Hz (still reasonably good)--being maintained automatically by the Isoch machine.
BUT, there's a chance the system load could continue to increase. And that means that the maximum power output of the Isoch machine's prime mover governor could exceed 25 MW. So, the WELL-TRAINED operator, under the guidance of the EXPERIENCED operations supervisor, decides to reduce the load on the Isoch machine. And, to do this the operator goes to one of the Droop machines and increases it's power output to 10 MW. The effect on the system as the load on this Droop machine is being increased is to increase the frequency of system (ALL the generators--including the Isoch machine's generator). BUT the Isoch machines prime mover governor AUTOMATICALLY reduces the load on the Isoch machine by the amount the load was increased on the Droop machine: 5 MW. And the system frequency (and that of all the generators synchronized to the system) was stable at about 50.07 Hz. The load on the Isoch machine is down to 19 MW, the load on one of the Droop machines is up to 10 MW, and the load on the remaining three Droop machines is unchanged at 5 MW--for a total of 44 MW.
I gotta stop here because Control.com has a maximum limit on the number of characters, and if I haven't exceeded the limit yet, I gotta be close.
TO BE CONTINUED.