In this setup, is it possible to operate all three generators in parallel by configuring DG-1, DG-2, and the STG in Droop mode, while operating DG-3 in Fixed kW mode?The manufacturer claims that DG-3 cannot run in parallel with 11kV generators, citing a mismatch in droop settings: the maximum attainable droop for DG-3 is 2%, whereas the 11kV generator has a 3% droop setting. Therefore, they argue parallel operation is not feasible. However, I believe parallel operation could still be possible if DG-3 is set to Fixed kW mode instead of Droop mode.
Additionally, are there any potential issues with running the STG in parallel with the diesel generators? What key factors should I consider to ensure stable and safe parallel operation?
Your insights and suggestions would be highly appreciated.