I'm working with an IDEC FC5A PLC that has an Analog input module (FC4A-J2A1). I'm running an ultrasonic level sensor to this input. I have checked the calibration of the sensor and verified its output is correct with a fairly accurate Fluke 87v. The input is set to scale 4-20 mA to a value of 0-84 and store that in a register.
If I have a value of 12mA for instance this should give me stored value 42, shouldn't it? I'm getting about half of that. So, I doubled the scale to be 0-168. That was much closer but still a bit low. I again changed the scale to 0-180 and now this seems to be pretty close.
I'm wondering if the IDEC Analog input module is just not reading accurately. I can't see what mA value it is reading. I can only see the scaled output value. Is there somewhere I can see the mA value the input is seeing?
If the module is just not accurate is there a calibration I can do?
Thank you.