Repeated Capacitor Failure on Single-Phase Pump Connected to Pressure Controller (230V)

I’m facing a recurring issue with a single-phase capacitor-run pump installed at a client's site. The pump is connected to a pressure controller, and within one month, we’ve had three breakdowns, each caused by a damaged capacitor. After multiple breakdowns, we replaced the entire pump with a new one, and the new pump experienced the exact same issue—capacitor failure within a short time. Here’s a detailed breakdown of the situation:
Pump Type: Single-phase capacitor-run pump.
Capacitor Failure: The capacitor burns out after a short period of operation (within 2 or 3 days).
Power Supply: The site operates on a standard single-phase (230V/50Hz) power supply, but there is a lot of solar electricity generation around the area and also at the client house, which is given to the common grid. but we haven’t yet checked for voltage fluctuations or instability.


Pressure Controller: The pump is controlled by a pressure controller. Could the controller be causing the issue?

Voltage Supply: We suspect possible voltage fluctuations due to solar electricity generation, but we haven’t recorded them yet. Could this be the primary cause?
Has anyone encountered similar issues with capacitor failure on pumps connected to pressure controllers? I would appreciate any help on where to begin troubleshooting or what checks to prioritize.
 
I agree with @Dave. The capacitor is just used for starting the single-phase motor, and should be "disconnected" when the machines accelerate above a certain RPM.

But, if the signal from the pressure controller is closing and the opening and closing multiple times in succession during starting this could be a part of the problem. Or it could be something else entirely and nothing to do with the signal from the pressure controller.

In general one wouldn't think a proper installation of a few photovoltaic solar panels with a good inverter (doesn't have to be the most expensive, but it should be of reasonable quality) wouldn't cause any problems with the pump motor as the pump motor shouldn't be continually starting and stopping, either. That could be part of the problem--the motor isn't rated for the number of starts/hour or per day; someone just chose the motor based on power and cost instead of considering duty. We really don't know the application (fresh water pump being used to supply a house or process?) and is it possible the system isn't properly configured (doesn't have an "accumulator" of some size to prevent frequent starts/stops)?
 
Grid was connected with Solar farm's Invertors which are foreseen that less of them install with Harmonic reduction. Harmonics from such Invertor export to the grid and may cause interfere Protection relay or Electronic device are being out of order or short life time. Install A.C. power filter which block the noise while passing the disired supply voltage to Pump is recommended.
 