sORRY BUT i DONT SEE THE RESERVE POWER Software Parameters Configuration..

Can you share it ...
Capture10.PNG
This is reverse power configuration. I see it set 35kW and dont have anymore.
Why dummy load control & Load shedding control are not enabled and adjusted ? is that ok for you?
answer: I dont know. All were set by manufacture according to our request.
What is the device with 16 pins on the left bottom of the single line diagramm is used for ?? with letters D L C J A H K F ,,...
answer: sorry. i also dont know.
thank you.
 
.Looks like the Diesel genset "take power" from the load bank ( The coolers and other s pumps " if connected together" for instance at your site )

Did you try to change time delay setting and see what happen ?? for example i see time delay adjusted to 2s what about changing it to 3s if OEM allow it for sure ...
 
Today's technology has made it possible to quickly and seamlessly switch between using your generator and other forms of electricity when needed. It is known as reverse power, allowing you to use your generator as an extra energy supply when there is an outage or brownout. Doing this can ensure that your home remains powered during difficult times while reducing your carbon footprint.
 
Amitbajpayee,

Please provide a link (or more than one) to a reference for your statements—either a website or document that states how a generator producing reverse power can be used to provide power for a home during “…difficult times….”

Thank you!
 