I want to map data between a Siemens S7 300 and an AB SLC500 series PLC. Anyone know how I can do this at minimum cost? Can't I use a Profibus card in each to tx the data and use code to map the data to the I/O?
I know of 3 options for exchanging data between Siemens S7 and SLC500:
1) Profibus-DP, as you state in your question. SST (Woodhead) makes scanners for the SLC backplane, one master and slave (SST-PFB-SLC) and one onl;y slave (SST-PFB-SLC-ADP). Easy to configure, easy to program. On both sides (Profibus-DP is native to Siemens, a SLC as Profibus slave is simple top configure).
2) A serial CP340/CP341 in the S7 can be configured to exchange over 3964R protocol; Prosoft makes a MVI46-3964R module for SLC PLCs. Slower exchange, in Siemens relatively easy to program (function blocks available), more complex in the SLC.