star-delta motorstarter

H

Thread Starter

Hp.Laager

we have installed star-delta motor starters for water pumps with 22.0kW AC 3-phases drives.
In the moment of switch from star to delta the circuit breaker before always release (trip).

Does anyone know this problem and can help me?

(Hint: motor connection is ok)
 
Sounds like the star and delta contactors are coming together. There should be a mechanical interlock between them and a star-delta timer controlling the switching.
 
Is this a "home built" motorstarter or a prefab?
There must be a short delay between the switching.
 
P

Paul Dackermann

Star-Delta is an open transition scheme. A time r with a N.C.T.O. contact is employed. (Hint: motor connection is ok) I am going to asked an off the wall question. If the connections are good; are the starters as recieved from the factory wired properly ? Verify the factory work. Is the transition set properly? It would be good to hear the outcome of the troubleshooting?

Regards,
Paul Dackermann
 
S

Steven Crichton

Although you have checked the motor connections, it has happenned to me twice before when the motor terminals were wrongly marked. You get a resistance across say v1 and v2 which makes you think that it is correct, but in reallity they have been swapped, ie v1=v2 and v2=v1. What happens is that it will start in star ok but when it changes delta you have one phase out of sync, which causes an over current. The only way i found out how to check for this was to swap them one at a time and then swapping them back before trying the next pair.
 