Two VFD with DC BUS use one braking resistor

I have two VFDs (same model), there is a DC bus between them. These two VFDs never work together, (another one is always stop when one is running). So, can These two VFDs share one braking resistor? When one motor is decelerating, will the regeneration power affects another one? Thank you!
 
You haven't indicated why the DC bus on both VFD are linked is this suggest dual usage.

As it stands only one resister is needed. Perhaps the idea was to have one motor decelerating whilst the other was running. One project I design/commissioned had motor 'pairs', one large the other small.
The DC busses were connected so when the client process commenced, the smaller motor was in permanent regen. mode sending power to the larger VFD.
 