I am working on the Rm7800 series for my new burner controller. The configuration that I have will be like:
PLC AB ControlLogix + HMI (FactoryTalk) --> Modbus bridge converter (Prosoft) --> RM7800L1053 + S7830A1005 + S7810M (Modbus communication module)
I would like to get a lot of status from the table 15 (7800 Series Sequence State Codes) to display in my HMI (like the status of valve, flame scanner, etc.). But the register 40003 will give me only 1 integer value at a time. How can I get the status I want to display on my HMI? (I am using FactoryTalk Studio)
This is the manual of the S7810M Honeywell Modbus Module
https://thermalsolutions.honeywell....dbus-module-datasheet-65-0249-7-nl05r1212.pdf
Thanks!
PLC AB ControlLogix + HMI (FactoryTalk) --> Modbus bridge converter (Prosoft) --> RM7800L1053 + S7830A1005 + S7810M (Modbus communication module)
I would like to get a lot of status from the table 15 (7800 Series Sequence State Codes) to display in my HMI (like the status of valve, flame scanner, etc.). But the register 40003 will give me only 1 integer value at a time. How can I get the status I want to display on my HMI? (I am using FactoryTalk Studio)
This is the manual of the S7810M Honeywell Modbus Module
https://thermalsolutions.honeywell....dbus-module-datasheet-65-0249-7-nl05r1212.pdf
Thanks!