voltage drop

E

Thread Starter

electrical

i have an 8oo foot run off cable i need to run that will be feeding a 120 supply of 100 va transformer. is the #12 rwu wire size adequate.

tom [at] duplexelectricalltd.com
 
Electric... voltage-drop and conductor-loss are 2.67-V, and 2.22-W. respectively.

If you want the calculation method, contact me off-list.

Regards, Phil Corso (cepsicon[at] aol [dot] com)
 