Background:
This is for KNPC. We have four units - mechanical drive fr 5002c. Control system is Mark 6 (TMR).
Unit # A - The unit was running, normal shutdown initiated to check faulty gas detectors in Turbine and filter House compartment.
FYI, almost 1 day back, faulty VCMI of another Unit # 3 was replaced with the VCMI of the Unit. Since customer was keen on starting that Unit# 3.
So now, For Unit # 1, Control is simplex since Only S and T are in control, R - Fail mode due to the VCMI.
Customer wanted to start the unit. Forced l3comm io for a start pass and started the Unit. Removed force
Now, VPRO [z] had diagnostics as
321 - g1/tnl_os_rpm
201 - l4etr1_fb voting mismatch
200 - l4etr2_fb voting mismatch
99 - Sol # 1 Voltage mismatch
100 - Sol # 2 Voltage mismatch
VTUR [T]
225 - tnl_rpm
Fault code 321 of VPRO [Z] and 225 of VTUR [T]was gone/reset after LP shaft attaining 70% of its speed. SP set at 70% (Before loading)
Q1) Suspect Protection is giving a Trip to the solenoids l20fg, l20fl. True/False?
Q2) Did the Emergency Trip relays failed on TREG?
Q3) Believe Protection is alos on simplex now. (Only VPRO X,Y) True / False?
Q4) Is it advisable to run the machine or inform the customer to Stop.?
Please your valued suggestion and advises are highly requested.
If customer agreed to stop, advise on what all to check, what all to replace etc..
Regards,
ARF
This is for KNPC. We have four units - mechanical drive fr 5002c. Control system is Mark 6 (TMR).
Unit # A - The unit was running, normal shutdown initiated to check faulty gas detectors in Turbine and filter House compartment.
FYI, almost 1 day back, faulty VCMI of another Unit # 3 was replaced with the VCMI of the Unit. Since customer was keen on starting that Unit# 3.
So now, For Unit # 1, Control is simplex since Only S and T are in control, R - Fail mode due to the VCMI.
Customer wanted to start the unit. Forced l3comm io for a start pass and started the Unit. Removed force
Now, VPRO [z] had diagnostics as
321 - g1/tnl_os_rpm
201 - l4etr1_fb voting mismatch
200 - l4etr2_fb voting mismatch
99 - Sol # 1 Voltage mismatch
100 - Sol # 2 Voltage mismatch
VTUR [T]
225 - tnl_rpm
Fault code 321 of VPRO [Z] and 225 of VTUR [T]was gone/reset after LP shaft attaining 70% of its speed. SP set at 70% (Before loading)
Q1) Suspect Protection is giving a Trip to the solenoids l20fg, l20fl. True/False?
Q2) Did the Emergency Trip relays failed on TREG?
Q3) Believe Protection is alos on simplex now. (Only VPRO X,Y) True / False?
Q4) Is it advisable to run the machine or inform the customer to Stop.?
Please your valued suggestion and advises are highly requested.
If customer agreed to stop, advise on what all to check, what all to replace etc..
Regards,
ARF