@Mohit.Sharama@ControlsGuy25
The relay setting and coordination is as per commissioning ( year1992). For electrical study , I'll get back to you, once I get hold of such document.
Plant SLD is attached. Generator AVR get's supply from shaft mounted PMG. No other excitation transformer is there.
Apart from AVR, no field boosting/flashing option is there.
Mohit
Thank you for this answer and clarifications.
So you got a self excited Generator with PMG .
Can we got a pic /schematic of the mentionned excitation system...for me even with PMG i use to see a separate excitation transformer for Boosting /field flashing durin event which need Voltage raise up /build up quickly...
Please have a read on how Voltage build up is done with self excited generator on that screenshot:
https://www.powerplantandcalculations.com/2020/05/pmg-excitation-avr-power-generation.html
How does the self excited DC generator build up its output voltage?
Due to flow of small current in the coil, an increase in magnetic field occurs. As a result, voltage output increases, in turn, increases the field current. This process continues as long as the electromotive force in the armature is more than the voltage drop in the field winding.
What is self excitation in generator?
A self-excited DC generator is the one whose field winding is excited by the current from the output of the generator itself. Depending upon the connection of field winding with the armature, the self-excited DC generators are of three types − Series Generator. Shunt Generator. Compound Generator.
Maybe ( thats just a guess ) that Protection on Overfluxing operated then AVR could not build up the nominal voltage
Do you confirm that you got such arrangement on these Generators?
James