add a 4 20 mA inputs / outputs in mkv

R

Thread Starter

Roberto

We need start a new system in our power plant (water injection system) on a ms6001b turbine, which is running on gas fuel.
Our control system is <I> mkv tmr.

I need to add a new analogics signal (4 - 20 mA) in the csp. for example an input pwq (water injection pressure from skid in the water plant) and an output wsrout (water injection control valve actuator).

All I need to know is the procedure to achieve that.

In other hand I want to know if it is possible add in demand display an input or output analogic with its units in miliamper.

thank you in advance.
 
When you read the Mark V Application Manual, GEH-5980, about adding inputs and outputs, what part(s) didn't you understand?

Have you researched similar signals in the Mark V and seen how they are assigned and scaled?

As for adding a signal to the Demand Display, have you read the Mark V User's Manual, GEH-5979? You can't change the engineering units of a signal, but you can easily add signals to any Demand Display.

 