Communication Problem for a Tsx Nano with PL7-07

  • Thread starter oronzo_canà
  • Start date
O

Thread Starter

oronzo_canà

I use Pl7-07 software under WIN98 O.S. , COM1 port and a TsxPcu1030 cable.

I changed all possible options in configuration/programming port and configuration/PLC version but i always receive the same error and PLC error led is always blinking (it's the first use of this PLC ).

Anyone can help me? Can it be a operating system compatibility of PL7-07 with win98?
 
This error appears if you are using PLC for the first time or if there is no program in the PLC. When you download a program in the PLC this error LED becomes off.You must follow the following steps:
1. Install Pl7 Software.
2. Install Unitelway Driver
3. Connect the cable between PC (Com1) and PLC (TER or AUX).
4. Make any dummy program and then download it in PLC.
 
A

Andreia Chiuratto

Hi,

I think that yes, do you see the address number of plc. The number have to be the same that your comunication... it's modbus?

I need for your help too. I need for table conversion of % I and %Q to hexadecimal or decimal numbers. Do you have?
Thanks.

Andreia Chiuratto
[email protected]
 