Hi! I have controller Eurotherm 3504. One of the thermocouples is not defined by controller as a B-type, it is identified as K-type. And we can’t change it for some reasons as a B-type. May be somebody had the same issue and can give me a piece of advice....Thanks
1) change the thermocouple in the process from B to K
2) use a -proper- temperature controller that supports all thermocouples, see: https://cascade.net/en/rb-series/
Thanks! It is the third thermocouple in controller...Other two are B and they work properly in this controller...it is a high temperature process and that is why I can't change thermocouple to K-type...
Ok, better test it all very well with a good thermocouple simulator so you're 100% sure the measurement is correct to avoid misreadings. Especially with a high process value alarm you must be 100% sure about the correct measurement!
Sounds like OP can't change the setting in the controller to reflect the actual TC type in the field. Is there a password lock on it? Some of those controllers let you lock parameter changes with a password that has to be entered into one of the parameters to unlock.