Since we did Combustion Inspection, we have been having this problem.We change all the liners and the cross fire tubes. The TC readings is as follows:
TTXD_1-394; TTXD_2-417; TTXD_3-417; TTXD_4-413; TTXD_5-415; TTXD_6-428; TTXD_7-425; TTXD_8-419; TTXD_9-415; TTXD_10-417; TTXD_11-416; TTXD_12-402; TTDX_13-400; TTDX_14-382; TTDX_15-372; TTDX_16-395; TTDX_17-394; TNH-101.16%; CTD-364deg C; TTXSPL-159.0; TTXSP1-56.1; TTXSP2-45.0; TTXP3-34.2; TTXM-408; WATT_EX-57.1
This is what we got after changing 7no thermocouples, and checking all the thermocouple lines. The Unit still alarm combustion trouble as it is approaching 60MW. Please what could be wrong?
TTXD_1-394; TTXD_2-417; TTXD_3-417; TTXD_4-413; TTXD_5-415; TTXD_6-428; TTXD_7-425; TTXD_8-419; TTXD_9-415; TTXD_10-417; TTXD_11-416; TTXD_12-402; TTDX_13-400; TTDX_14-382; TTDX_15-372; TTDX_16-395; TTDX_17-394; TNH-101.16%; CTD-364deg C; TTXSPL-159.0; TTXSP1-56.1; TTXSP2-45.0; TTXP3-34.2; TTXM-408; WATT_EX-57.1