Our valve position actuator had a pt100 4-20mA transmitter. now the new actuator's 4-20mA feed back unit is not reading on our circuit.
makers advised to fix a passive isolator between new actuator and the existing system. but the reading is valve close shows 4 mA and open shows 5.05 mA instead of 20mA.
The path is follows:
From 24vdc power supply +ve to the +ve of 4-20mA transmitter and -ve of the transmitter to +ve of Analogue display (shows 0-100pct valve open position) and its -ve to a diode/resistor module (+ve) and the -ve of diode is connected to a AI Analogue input card (Wago 750-468 (4IANA1). The 24v power supply -ve is connected to AI input cards common negative.
where exactly the passive isolator can fix so as to get the reading on input card? If only the analogue meter is connected to only to the new 4-20mA transmitter then the reading is correct valve close 4mA and open 20 mA and meter shows 0 to 100pct.
Please advise.
makers advised to fix a passive isolator between new actuator and the existing system. but the reading is valve close shows 4 mA and open shows 5.05 mA instead of 20mA.
The path is follows:
From 24vdc power supply +ve to the +ve of 4-20mA transmitter and -ve of the transmitter to +ve of Analogue display (shows 0-100pct valve open position) and its -ve to a diode/resistor module (+ve) and the -ve of diode is connected to a AI Analogue input card (Wago 750-468 (4IANA1). The 24v power supply -ve is connected to AI input cards common negative.