what is duration for ignition timer of spark plug in gas turbine frame-5 during start up?
V Thread Starter vimal gupta Jan 3, 2011 #1 what is duration for ignition timer of spark plug in gas turbine frame-5 during start up?
3 309EGuy Jan 3, 2011 #2 For gas fuel K2FGAS is normally 10 seconds, and for Liquid fuel K2FLIQ is 30 seconds. I have seen these values used on Frame 5/6B/7E/9E turbines. If all things are working well flame typically occurs within a couple seconds for gas and 8-10 for liquid fuel.
For gas fuel K2FGAS is normally 10 seconds, and for Liquid fuel K2FLIQ is 30 seconds. I have seen these values used on Frame 5/6B/7E/9E turbines. If all things are working well flame typically occurs within a couple seconds for gas and 8-10 for liquid fuel.
CSA Jan 3, 2011 #3 The length of the ignition timer is dependent on the application and sometimes on the fuel being started on.
The length of the ignition timer is dependent on the application and sometimes on the fuel being started on.
V Volkan AKIN Jan 3, 2011 #4 fire has to occur at most 30 second, otherwise it trips. but in generally you need 3-5 second to observe fire..