our site fuel oil system is as
1- Fuel oil forwarding skid two centrifugal pumps take fuel from storage tank and send towards Gt
2- Heating skid-electric heater for heating if temp of oil is low
3- filtering skid regulate and filter the oil
I paste the system description below. since the site is in commissioning, first psv at filtering skid was operating continuously, setting of psv is 12 bar while forwarding pump discharge is 8 bar. installed new psv it was also doing same
there is a pressure regulating valve which reduce pressure around 5 bar with reference pressure of air (PRV is differential pressure type). there is a gauge at which measure outlet pressure of skid. there is pressure variation continuously around 4 to 6 bar.
following have been checked but no final result
1-accumulator pressure
2-PRV
3-Saytems NRV
4-forwarding pump suction stainer
5-Air bleeding
another, when there is hunting in system, Same time fuel flow at local flow counter stops but there is no trouble inside GT operation. This equipment is subject to European directive 97/23/EC (pressure equipment directive (PED) and 94/9/EC (Equipment for use in potentially explosive atmospheres).
* One safety valve (PSV351) protects the upstream circuit against an eventual over pressure if isolating valves are closed at the same moment and the fuel temperature increases.
Adjustment: 12-bar g ( +0/-1,2bar) / 174PSI . (+0/-17,5)
* One skid isolating valve (HV302).
* One regulating system to control the Distillate fuel oil pressure at GT inlet. It is constituted of one main regulating valve (PCV 355 piloted by air pressure reference), one needle valve (HV 355), two reverse mounted spring loaded check valves (NV355A, NV355B).
* One air pressure regulating valve (AFRG355) with filter automatic drain and pressure gauge gives a pressure reference to the regulation valve PCV355. Setting: 4.5 barg.
* One pneumatic valve (FV363), normally open, is necessary to insure a minimum flow for pump pressure regulating valve, and heater if any, during the start up with fuel oil (when the stop of valve FV359 and PCV355 are closed ).
* Two filters (FLT 301,FLT 302), one in operation and the other in stand-by, equipped with:
- Four isolating valves (HV303, HV304, HV311, HV312),
- One balancing valve (HV306)
- One drain valve or each body (HV308, HV310)
- One vent valve for each body (HV307, HV309)
- One safety valve for each body (PSV361, PSV362), only for thermal expansion Adjustment: 10-bar g ( +0/-1bar)
For TG type, each filter body contains:
- 9 synthetic cartridges, ß17 = 200, Ref: PH.718.01.CN.
* One accumulator (ACC 301) absorbs sudden fuel pressure variations at GT inlet. Typ of TG Distillate fuel oil
9E 2,5 bar g / 36 PSI
* One pressure accumulator isolating valve (HV318). since site is in commissioning,
1- Fuel oil forwarding skid two centrifugal pumps take fuel from storage tank and send towards Gt
2- Heating skid-electric heater for heating if temp of oil is low
3- filtering skid regulate and filter the oil
I paste the system description below. since the site is in commissioning, first psv at filtering skid was operating continuously, setting of psv is 12 bar while forwarding pump discharge is 8 bar. installed new psv it was also doing same
there is a pressure regulating valve which reduce pressure around 5 bar with reference pressure of air (PRV is differential pressure type). there is a gauge at which measure outlet pressure of skid. there is pressure variation continuously around 4 to 6 bar.
following have been checked but no final result
1-accumulator pressure
2-PRV
3-Saytems NRV
4-forwarding pump suction stainer
5-Air bleeding
another, when there is hunting in system, Same time fuel flow at local flow counter stops but there is no trouble inside GT operation. This equipment is subject to European directive 97/23/EC (pressure equipment directive (PED) and 94/9/EC (Equipment for use in potentially explosive atmospheres).
* One safety valve (PSV351) protects the upstream circuit against an eventual over pressure if isolating valves are closed at the same moment and the fuel temperature increases.
Adjustment: 12-bar g ( +0/-1,2bar) / 174PSI . (+0/-17,5)
* One skid isolating valve (HV302).
* One regulating system to control the Distillate fuel oil pressure at GT inlet. It is constituted of one main regulating valve (PCV 355 piloted by air pressure reference), one needle valve (HV 355), two reverse mounted spring loaded check valves (NV355A, NV355B).
* One air pressure regulating valve (AFRG355) with filter automatic drain and pressure gauge gives a pressure reference to the regulation valve PCV355. Setting: 4.5 barg.
* One pneumatic valve (FV363), normally open, is necessary to insure a minimum flow for pump pressure regulating valve, and heater if any, during the start up with fuel oil (when the stop of valve FV359 and PCV355 are closed ).
* Two filters (FLT 301,FLT 302), one in operation and the other in stand-by, equipped with:
- Four isolating valves (HV303, HV304, HV311, HV312),
- One balancing valve (HV306)
- One drain valve or each body (HV308, HV310)
- One vent valve for each body (HV307, HV309)
- One safety valve for each body (PSV361, PSV362), only for thermal expansion Adjustment: 10-bar g ( +0/-1bar)
For TG type, each filter body contains:
- 9 synthetic cartridges, ß17 = 200, Ref: PH.718.01.CN.
* One accumulator (ACC 301) absorbs sudden fuel pressure variations at GT inlet. Typ of TG Distillate fuel oil
9E 2,5 bar g / 36 PSI
* One pressure accumulator isolating valve (HV318). since site is in commissioning,