I am sayin tha PMS can be not well setted for frequency control mode..
Contrôle de la vitesse de chute litterally.. stand for droop mode CSA..By the way, ControlsGuy25, what is the French word or term for “Droop Speed Control”? Inquiring minds would very much like to know.
@gubavac111 Thank for your reply..@ControlsGuy25 and @CSA
Thank you sooo much for your input!
Since I am not on your level of expertise, I will need some time to read several times what you have written and then some time to try to understand it, so I can provide you with the best possible information.
Once again, thank you so much, it means a lot to me!
Maybe load sharing scheme is not tuned properly ..
Search for event trigger SOE event list alarms messages if available it should withc Cimplicity..
Can you check the SLD (first drawing that you shared ) it seems that it is written 2 times GENERATOR pPORTSIDE INSTEAD OF ONE OF THEM ATLEAST Would be written STANDBOARD SIDE as per you description ...
Can you confirm..
gubavac111,
IF the PMS is not set up correctly AND it is trying to control frequency when only one genset is online, that could be part of the problem.
Opinions--and ass-u-me-ptions--are worthless when troubleshooting technical issues, and can cause lots of wasted time and effort. If you don't know how the PMS works, you should start finding out how it works, and when.
IF the PMS were NOT working when there was only one genset online, then that genset's governor should be in Isochronous Speed Control Mode. And, if a second genset were to be synchronized to the first, then the one of the gensets should be in Isochronous Speed Control Mode and the other should be in Droop Speed Control mode OR they both should be in Droop Speed Control Mode (or some form of Isoch Load Sharing mode--which is really just de-tuned Isoch, very close to Droop) AND the PMS should be sending signals to one or both gensets to try to control frequency as load changes.
You MUST understand how--and when--the PMS works.
You have also NOT told us if this scheme ever worked properly since sea trials/commissioning, or if it's always behaved this way.
My money is on EITHER poor maintenance of the diesel fuel control rack/system, OR the PMS--and based on my poor experience with many PMSs (especially ones that are custom, one-off systems and not "standard" off-the-shelf systems)--it's more than likely the configuration/programming of the PMS.
There's one fairly simple way to test this--and that's to turn off the PMS and have a well-trained operator or two monitor the gensets. One genset should be in Isoch mode, and any other gensets added to the island (what you want to call a "grid") should be in Droop Speed Control mode. That would be a very simple test. But the operator(s) have to understand how to adjust the gensets in a multi-unit configuration to keep the load on the Isoch unit from being too high or too low as HVACs and other loads on the island are switched on and off.
But, it's not likely that anyone will agree to this test. Because no one thinks the automation (PMS) could be at fault. Not to mention it's kind of risky if the operator makes a mistake (think black-out...).
So, the speculation will continue.
Get familiar with the configuration and programming of the PMS--especially if it's a custom, one-off design. If it's a "standard" off-the-shelf system, get the manual and the drawings (schematics) out and start reading and studying (another reason NOT to go with a custom, one-off PMS: the documentation is usually pretty difficult to find, read, and understand).
Best of luck!
That would be great to know OEM controller /type /model..First of all, I can't believe you are this kind to write in so many details to try to help me. It's just amazing!
I have one small observation that might be helpful:
When observing Local operating panel (the panel where you can operate genset locally and see engine and alternator parameters) of the genset that was online, I could see that the command to INCREASE SPEED or DECREASE SPEED was given every 7-8 seconds, but the frequency was fluctuating just as usual during these 7-8 seconds, going up and down. And the command to increase or decrease speed is, from what I've seen, given by the PMS.
So, it could be that, as you mentioned, there is an issue with the poor maintenance of the diesel fuel control rack/system and perhaps not with the PMS.
Wow, what a wealth of information! Please excuse me for not replying quickly. I am quite busy right now as we are entering dry dock tomorrow and will reply as soon as I process your info. Thank you!Here's a little example of how a system WITHOUT a PMS might work. (By the way--the original poster has used the terms "PMS" and "load sharing" interchangeably--they might be similar, but we have mostly been talking about frequency control, which is what we have been mostly asking about. Be careful with terms; just like using "grid" to describe the generation/transmission/distribution system on the ship--which is not generally referred to as a grid, like on shore generation/transmission/distribution systems are.)
Let's say the yacht is off shore, admiring the coastline from afar, and is not connected to shore power. It's early morning and the HVAC is not really in use; just some fans and lights and water pumps (bilge pumps; cooling water pumps; RO pumps; espresso machine; and a tea kettle; and the navigation gear). So, only one generator is running, and it is about 50% of rated output and the frequency of the yacht's electrical system is about 50.09 Hz. The final condition is the genset's governor is operating in Isochronous Speed Control mode--meaning that it will change the fuel flow to the diesel to make the frequency stay as close to 50 Hz as possible as long as the total load on the yacht doesn't exceed 100% of the genset's rated capacity, nor fall below 0% of the genset's rated capacity. Isoch Speed Control will do that (maintain 50 Hz)--all by itself. No operator intervention required--as long as the load on the yacht doesn't exceed the limits (0% and 100%) of the genset rating (and that's the PRIME MOVER rating--NOT the generator nameplate rating; gensets are rated based on prime mover capability not generator capability). It's also VERY IMPORTANT that when operating in Isoch mode an operator can't do anything to the genset to change the load on the genset. If the operator clicks on RAISE (or INCREASE) all he/she will be doing is increasing the frequency setpoint--which will raise the generator output frequency and the speeds of the diesel and generator--but the load WILL NOT change. The load will only change as electrical devices (motors; microwaves; navigation gear; lights; HVAC) are turned on or off, which will tend to cause the frequency to change--but Isoch mode won't let it change (as long as the total amount of electrical devices doesn't exceed 100% of the genset rating nor drop below 0% of the genset rating).
As people wake up and start using more electricity the load on the yacht's system will increase. The engineer on watch is monitoring the generator output and the yacht system load and it's starting to increase. As the load approaches 85% of the rating of the genset the engineer's instructions are to start and synchronize a second generator, which he does--and his instructions also say the second genset's governor is to be in Droop Speed Control mode after synchronization with the first genset. Further, his instruction say to then reduce the load on the Isoch genset to 45% of its rated capacity. So, the experienced and well-trained operator increases the load on the Droop genset until the load on the Isoch genset drops to 45% of its rated capacity. (Because one cannot directly change load on a genset running in Isoch mode; so the way to indirectly change the load on an Isoch genset is to change the load on one or more Droop gensets synchronized to the Isoch genset.)
As the sun rises and the below-deck spaces heat up, the HVAC units kick into higher output--raising the load on the yacht's systems. Also, it's decided to raise anchor and motor slowly to another location for the afternoon, so some other electrical devices are started--further increasing the total load on the yacht's system. The engineer on watch is monitoring everything that's going on and notices that the load on the Isoch genset is again approaching 85% of rated, but that the load on the Droop genset hasn't changed (which is as it should be!). So, to reduce the load on the Isoch unit the engineer on watch increases the load on the Droop machine.
Once the new anchorage is reached, and the anchor dropped, and the engines shut off, the load on the yacht's system drops a little, thereby reducing the load on the Isoch genset. The engineer on watch monitors the system and when the load on the Isoch unit gets down to about 15% of rated his operating instruction tell him to increase the load on the Isoch genset--which the engineer on watch does by reducing the load on the Droop genset. The load on the Isoch unit now increases to about 55% of rated, and the load on the Droop unit falls to about 25% of rated or so. (In a small, island system, the load on the Droop genset doesn't change unless the operator changes it. The load on the Isoch genset changes automatically--but only because if it didn't the system frequency would drift away from nominal. It's not the amount of load that's making the Isoch unit change its power output, it's what the amount of load does to the frequency that makes the Isoch unit change its power output. The Droop unit? It's just "along for the ride" (presuming the Isoch governor is working properly); it's load won't change unless an operator changes it. (I'm talking a very small, manually controlled power island. And, it works similarly for larger systems as well, though it's not as easy to understand or explain--but it's still the same principle.)
This is how load is "shared" between gensets in a manual way. (I prefer to call it "load balancing.") Remember: The load of a genset running in Isoch mode can't be directly changed (using the Isoch's governor)--so the only way to change the load on the Isoch genset is to do so indirectly by changing the load on a Droop genset synchronized with the Isoch genset. The Isoch genset governor will sense the change in frequency and will automatically adjust the fuel flow-rate to the Isoch's prime mover to keep the Isoch generator output--and so the that of the yacht's system--at 50 Hz.
There's usually a little "deadband"--sometimes called hysteresis. I'm talking about a difference of approximately +/-0.10% of frequency, so a rather insignificant amount. If you hook up a multimeter capable of reading frequency to a shore-side electrical outlet you will see that over the course of a day, any normal, usual day, the frequency will NEVER stay exactly at 100.0% of rated--it's always a little above or a little below. That's normal, but what the original poster described is not normal and is excessive.
This is what a PMS is supposed to do--look at a set of operating instructions for maintaining the frequency of a small, "islanded" power system, and make the necessary adjustments to make it all happen seamlessly in the background. Need more power? Start and synchronize a second genset. Maintain some kind of balance between multiple gensets (usually there's some kind of table or matrix which defines usage rates/times/capacities for the various generators). Change the "lead" and "lag" generators automatically. And, it's not as easy as a lot of people think it is. Not at all. Especially when all of the genset governors are usually operated in Droop Speed Control or some kind of "Isoch load-sharing" mode. The latter actually complicates things (in my personal opinion--a LOT), but then so does the timing of pulses to change load on multiple machines.
The original poster said his hunch was the PMS wasn't active when only on genset was running. That is an ass-u-me-ption--not a bad one, necessarily, but an ass-u-me-ption nonetheless. Personally, I've only seen a couple of PMSs that will switch genset governor mode between Isoch and Droop--it's just not common, but it does happen. Generally, the implementers of PMSs think the genset governors should always remain in the same mode--AND they think the genset governors are NEVER as capable or intelligent at the PMS so they want the PMS to ALWAYS be in control, whether it's a single genset or two or three or more.
And, it can--and usually does--get very complicated very fast.
Now, imagine what happens to system response when the diesel genset fuel racks/injectors are not being properly maintained. Or the diesel fuel filters get some water or dirt in them, choking the flow through the filter(s)--and they aren't swiftly replaced. Ir the diesel air filters get dirty, or the turbos get worn. People forget how all of these components and systems have to work together. But, because the "control system" has so many wires and LEDs and it's SOOO complicated--well, it just has to be the control system that's the problem. (And in the case of many custom, one-off PMS control systems--they can definitely be the problem, though convincing the supplier is next to impossible--if they're even still in business or still working on PMSs!).
The purpose of a PMS is to do the above--maintain frequency without exceeding the limits (minimum or maximum) of the genset(s), and keep the genset(s) from operating too close to their limits (minimum or maximum). Isochronous and Droop Speed Control can do the first (maintain frequency)--but they require trained and experienced operators to do so, and in the process the operator(s) will also be "sharing" loads between the gensets. Replace the operators with a PMS, and, you damn well better know exactly what the operators would be doing--and change the genset governor modes in the process, and well, you have greatly increased the complexity of the PMS.
Hope this helps! It's just a small window into what goes on all day every day around the world in many places, and at sea.
@gubavac111 Can you share a quick feedback on the status at site /yacht...Regarding that issue that you posted here.@ControlsGuy25 and @CSA
Thank you sooo much for your input!
Since I am not on your level of expertise, I will need some time to read several times what you have written and then some time to try to understand it, so I can provide you with the best possible information.
Once again, thank you so much, it means a lot to me!
Hi,@gubavac111 Can you share a quick feedback on the status at site /yacht...Regarding that issue that you posted here.
ControlsGuy25