HiHi,
We are currently in the shipyard, connected to shore power because our gensets are being overhauled.
Of course, frequency is now very stable at 50.02Hz.
Okay !
HiHi,
We are currently in the shipyard, connected to shore power because our gensets are being overhauled.
Of course, frequency is now very stable at 50.02Hz.
Sorry to disappoint you.Ok so since more than 2 weeks that we did not hear from original poster ..
So we can say that this thread is closed...
Unfortunately we were ready to support and doing good efforts ..but sometimes here People just leave without any feedback....
Thank you for you reply...S
Sorry to disappoint you.
I have neglected this topic despite all your help.
My contract on the ship ended and I went home.
We stopped troubleshooting this problem and just left it as it is. It still persists, but we will do nothing about it.
That is the summary.
You sure paralleling with Grid?I work onboard a yacht where we have 3 pieces of 765kVA diesel gensets composed of the engine MTU 12V2000 M51A and the alternator Stamford HCM634J2. The gensets are producing 3 phase 400VAC/50Hz.
First of all, I am not sure if there is even a problem with the gensets so here goes my first question:
1. What is the allowed frequency tolerance on these type of gensets or on diesel gensets in general?
Our frequency varies less than 1%, but even that is enough to cause problem with our Main UPS and Fire detection system which are sensitive to input power quality. Because of frequency variation, UPS does an automatic bypass (just transfers input immediately to the output) and Fire detection system has a Power input quality fault. Btw, UPS' tolerance to the input power can be adjusted and it is already at the max, although I don't know what the max is because it was done 2 years ago by the service technician on some potentiometer deeeeep inside the UPS.
So...this is the situation:
When gesets are working off the grid, their frequency is super stable.
When any of them is connected to the grid, there is a frequency fluctuation.
When 2 of them are connected, fluctuation is smaller and when all 3 are connected, fluctuation is smallest, but still bigger than when they are running off the grid.
Below table shows readings when only one of the gensets was connected to the grid. So, for example, when just Centre genset was connected, genset frequency (which is in that case grid frequency as well) varies between 49.67 and 50.33 Hz, current varies fluctuates around 50A and power around 25kWA.
f, kW & A readings (Analog meters) Port generator Center generator Starboard generator Time frame measurement Frequency on power analyzer 49.75 to 50.15 Hz 49.67 to 50.33 Hz 49.63 to 50.28 Hz 30 sec Ammeter readings on the main switchboard 50 A
fluctuation 50 A
fluctuation 50 A
fluctuation 18 sec kW readings on the main switchboard 25 kW
fluctuation 25-30 kW
fluctuation 25 kW
fluctuation 25 sec Voltage fluctuation on all three generators is from 400 to 402 VAC
2. Do you have any idea what might be causing this kind of behavior?
ControlsGuy25,
I think two things are going on here. First, the yacht is in drydock and gubavac111 is quite busy. Being in drydock also means the yacht is connected to shore power only, so the diesel gensets are not being used, AND he has said they are undergoing maintenance (probably changing oil, filter(s), testing compression, possibly even testing or replacing fuel injectors). It has been suggested that the problem could possibly be due to sluggish diesel governor response (or dirty fuel filters, etc.). So, it seems gubavac111 is kind of waiting to see how the units respond to islanded operation AFTER drydock, or maybe during some of testing before leaving drydock.
Second, I think gubavac111 is trying to find time to digest some of what's been written and try to apply it to his understanding and investigation of how the PMS on the yacht performs, and how the diesel governors are configured, etc.
And, all during drydock, which can be a very trying time--because time in a drydock is money, and so it's best to get in an get out as quickly (and inexpensively) as possible. Which leaves little time for reading and investigation.
But, it will end soon enough, and once the yacht is afloat and gets separated from shore power and needs to use the on-board generators we will get some feedback.
What I wish we knew was if this problem of frequency instability has been around since the original commissioning of the gensets, or if it's something which has started "recently" or has gotten worse with time since original commissioning. This would kind of point to either something with the diesel governors or fuel/air supply (dirty filters; bad injectors; loose or sluggish fuel rack(s); etc.), or to the PMS configuration and programming.
But, alas. Patience is a virtue, eh? And how many of us are virtuous?
HiHello again!
I just wanted to give a small update since I am back on the yacht.
So, the gensets overhaul didn't help - the issues still persists.
CSA, you understand very well what dry dock is!
Looking through handovers of my past colleagues all the way to 2014, there is no mention of this issue.
That, however, doesn't mean the issue didn't exist, it might mean it was simply unnoticed because it didn't cause any real trouble in day-to-day operation.
I would LOVE to dive into this issue and just tackle it for 4-5 days, but that is just not possible with so many things going on in here.
When a guest pays 1.5 million USD for a one-week charter, the service must be superb and the tiniest detail must be taken care of - and this takes time.
Perhaps, there will be an opportunity in the future to work on this issue.