I presume the engine would be producing heat and PID controller would be controlling cooling water. To increase temperature, controller output would need to decrease water flow.Is the controller's output at 100%?
Can you put the controller into manual mode and force the output to 100%? Does the temperature then increase?
Yes, Patrick, good list of questions.First thing I always ask in cases of this:
A) what has been changed since the last time it worked ok?
B) what has been replaced?
Putting the controller on 100% manual output is a very good one. Try to check whether the problem is the electronics or the mechanics.
david_2 already gave the advice I would give. Here are a few extra ones if those ones don't check out:
1) can you connect a calibrator to the sensor wires to check the sensor itself?
2) check the measurement input on the PID controller by connecting a calibrator/simulator instead of the sensor
3) what kind of sensor are you using? Thermocouple (what type? K?), Pt100 RTD (very sensitive to vibrations). If the thermocouple is replaced with another type: verify if the thermocouple is of the same type (K?). If you are not sure check thermocouple with glass of 100°C boiling water with sensor connected to calibrator.
4) if there is a short circuit inside the thermocouple sensor tube you will have a misreading since the measurement point is not at the tip of the sensor.
5) is the jacked controlled with a heating element? Disconnect and check the ohm value and determine of the heating element is still ok
6) is the jacked controlled with valves: check the valves for operation (maybe valve needs cleaning)
7) is there a pipe clogged? Can you check flow of liquids?
8) are you at sea? What parts do you have at hand? PID controller (same type?) valves? sensors?
I hope you can find the problem by checking these things out.
Please let us know how things are going, maybe we can give you further advice.
| Thread starter | Similar threads | Forum | Replies | Date |
|---|---|---|---|---|
| F | ABB TZIDC Digital positioner no reach the auto adjust | Control Valves | 0 | |
|
|
Droop adjust and deadband mode control | Power Generation | 6 | |
| C | Mark V constant adjust | Power Generation | 9 | |
| G | adjust axial bently nevada probes | Process Control | 9 | |
| K | Twido Adjust Software | Programmable Logic Controller - PLC | 0 |