After I removed the resistor on the converter, the result remained the same, checksum errorDo you have an ohm meter (multimeter)?
It's possible the MCB also has a termination resistor enabled or permanently installed. You could confirm this by powering the device off, disconnecting the wires from the A and B terminals, and measuring the resistance between A and B. If it measures near 120 ohms, then it has a termination resistor, so you would also need to disable or remove this.
If possible, it may be better to connect biasing resistors. You don't have to use exactly 680 ohms, you could probably use anything from between approximately 500 ohms to 1k ohms. They should just both be the same.
this is my mainboard you can see it
Attachments
-
343.1 KB Views: 10