We can limit the minimum load for gas turbine at combined cycle when we active the primary fre
Thank you for replyHamada ramadan,
It's my understanding of the GE PFR (Primary Frequency Control) that there is no way to limit the minimum load. There may be some unusual or new logic/sequencing/application code, but when the grid frequency is unstable there is no way to limit the frequency excursions of the generator (and speed excursions of the turbine) nor is there any way to limit the changes in load. And, to be honest, doing so would be the opposite of what needs to happen when the grid frequency is not stable. One of the main concepts of Droop Speed Control is that it varies the fuel flow-rate (to gas turbines) as necessary to help support grid stability when the frequency is higher or lower than nominal. A failure to do so can result in black-outs, which are bad for everyone--the consumers of electricity as well as the producers.
EVERYONE wants the output of their turbine-generator to be stable and not change when the grid frequency is unstable--but that's just not the way AC power generation and Droop Speed Control work. That's not the way they are designed or implemented. And trying to hold output constant, or prevent dropping below a certain value--especially with turbines equipped with DLN combustors--is not good for the grid or for the turbines.
If you could explain a little more about your situation (because your original post is unfinished), we might be able to understand things a little better.
You should know that most people want to operate their GE-design heavy duty gas turbine in Pre-Selected Load Control mode--because they FALSELY believe if they don't the unit load will drift up and down "uncontrollably" and unit load will NOT remain stable (when the grid frequency is stable). Some grid operators and utility regulators have come to learn that operating in Pre-Selected Load Control at ALL times will prevent the unit from properly responding to grid fluctuations and actually contribute to grid instability, worsening the situation, by trying to maintain a stable load when frequency is more or less than rated or is fluctuating. The grid operators and utility regulators have, in many places in the world, decreed that Pre-Selected Load Control cannot be used at all times when synchronized to a grid. So, GE developed PFR (Primary Frequency Response) which detects frequency excursions while operating in Pre-Selected Load Control and allows the unit to properly respond to grid frequency disturbances. It's not an ideal situation, nor is it the best solution.
Pre-Selected Load Control was never designed to be used to operate GE-design heavy duty gas turbine at all times when producing power; it was designed as a way for the operator to input a desired load setpoint and let the turbine control system load (or unload) the unit in a smooth ramping fashion until the desired load was achieved, and then it should be disabled. Because, as long as the grid frequency remains stable the gas turbine-generator power output is going to remain stable--without Pre-Selected Load Control. However, when grid frequency deviates from nominal it is because of some imbalance in load and/or generation and if generators and their prime movers don't respond appropriately then, as was written, it can lead to black-outs. Pre-Selected Load Control, if left enabled and active--without PFR!!--over-rides Droop Speed Control. Worse, there is fighting between Pre-Selected Load Control and Droop Speed Control, which is one of several reasons that operating with Pre-Selected Load Control enabled and active--without PFR!!--actually worsens grid frequency problems.
To synchronize and operate multiple generators and their prime movers to a grid it is necessary for them to be operated in Droop Speed Control--this is the governor mode that allows multiple units of all sizes and capabilities to stably operate in parallel with each other when synchronized to a grid. It has been so since the beginning of AC power generation, transmission and distribution. People who believe (falsely) that their generator output should remain stable while the grid their generator and prime mover are synchronized to is unstable simply do not understand basic AC power generation fundamentals and live in an alternate world. It just doesn't work that way, and to even have a chance of stabilizing an unstable grid it is necessary for generators and their prime movers to respond and vary their output as necessary. It's physics and maths--and it can't be changed for one unit, or two or seven.
If the power plant where you work supplies a process plant independently of the grid, or exports a small amount of power to the gird while supplying an independent load (usually called an "island"), there are ways to mitigate the effects of grid frequency disturbances (they are not always desirable or easy--but there are some things which could be done depending on the situation). But, again, your original post was cut short, and we don't know the entire situation. But if you're attempting to ask if the minimum load of a gas turbine-generator operating with Pre-Selected Load Control AND PFR (Primary Frequency Response) enabled and active during grid frequency disturbances, the most probable answer is no, not with typical logic/sequencing/application code. And, probably not even with unique logic/sequencing/application code. If the GT load drops excessively and opens the generator breaker, or even results in flame-out of the gas turbine, then I would suggest some of the protective relay settings need to be checked and adjusted to prevent that, maybe even tripping the generator breaker open proactively.
Hope this helps!
In combined cycle modeHamada ramadan,
It's my understanding of the GE PFR (Primary Frequency Control) that there is no way to limit the minimum load. There may be some unusual or new logic/sequencing/application code, but when the grid frequency is unstable there is no way to limit the frequency excursions of the generator (and speed excursions of the turbine) nor is there any way to limit the changes in load. And, to be honest, doing so would be the opposite of what needs to happen when the grid frequency is not stable. One of the main concepts of Droop Speed Control is that it varies the fuel flow-rate (to gas turbines) as necessary to help support grid stability when the frequency is higher or lower than nominal. A failure to do so can result in black-outs, which are bad for everyone--the consumers of electricity as well as the producers.
EVERYONE wants the output of their turbine-generator to be stable and not change when the grid frequency is unstable--but that's just not the way AC power generation and Droop Speed Control work. That's not the way they are designed or implemented. And trying to hold output constant, or prevent dropping below a certain value--especially with turbines equipped with DLN combustors--is not good for the grid or for the turbines.
If you could explain a little more about your situation (because your original post is unfinished), we might be able to understand things a little better.
You should know that most people want to operate their GE-design heavy duty gas turbine in Pre-Selected Load Control mode--because they FALSELY believe if they don't the unit load will drift up and down "uncontrollably" and unit load will NOT remain stable (when the grid frequency is stable). Some grid operators and utility regulators have come to learn that operating in Pre-Selected Load Control at ALL times will prevent the unit from properly responding to grid fluctuations and actually contribute to grid instability, worsening the situation, by trying to maintain a stable load when frequency is more or less than rated or is fluctuating. The grid operators and utility regulators have, in many places in the world, decreed that Pre-Selected Load Control cannot be used at all times when synchronized to a grid. So, GE developed PFR (Primary Frequency Response) which detects frequency excursions while operating in Pre-Selected Load Control and allows the unit to properly respond to grid frequency disturbances. It's not an ideal situation, nor is it the best solution.
Pre-Selected Load Control was never designed to be used to operate GE-design heavy duty gas turbine at all times when producing power; it was designed as a way for the operator to input a desired load setpoint and let the turbine control system load (or unload) the unit in a smooth ramping fashion until the desired load was achieved, and then it should be disabled. Because, as long as the grid frequency remains stable the gas turbine-generator power output is going to remain stable--without Pre-Selected Load Control. However, when grid frequency deviates from nominal it is because of some imbalance in load and/or generation and if generators and their prime movers don't respond appropriately then, as was written, it can lead to black-outs. Pre-Selected Load Control, if left enabled and active--without PFR!!--over-rides Droop Speed Control. Worse, there is fighting between Pre-Selected Load Control and Droop Speed Control, which is one of several reasons that operating with Pre-Selected Load Control enabled and active--without PFR!!--actually worsens grid frequency problems.
To synchronize and operate multiple generators and their prime movers to a grid it is necessary for them to be operated in Droop Speed Control--this is the governor mode that allows multiple units of all sizes and capabilities to stably operate in parallel with each other when synchronized to a grid. It has been so since the beginning of AC power generation, transmission and distribution. People who believe (falsely) that their generator output should remain stable while the grid their generator and prime mover are synchronized to is unstable simply do not understand basic AC power generation fundamentals and live in an alternate world. It just doesn't work that way, and to even have a chance of stabilizing an unstable grid it is necessary for generators and their prime movers to respond and vary their output as necessary. It's physics and maths--and it can't be changed for one unit, or two or seven.
If the power plant where you work supplies a process plant independently of the grid, or exports a small amount of power to the gird while supplying an independent load (usually called an "island"), there are ways to mitigate the effects of grid frequency disturbances (they are not always desirable or easy--but there are some things which could be done depending on the situation). But, again, your original post was cut short, and we don't know the entire situation. But if you're attempting to ask if the minimum load of a gas turbine-generator operating with Pre-Selected Load Control AND PFR (Primary Frequency Response) enabled and active during grid frequency disturbances, the most probable answer is no, not with typical logic/sequencing/application code. And, probably not even with unique logic/sequencing/application code. If the GT load drops excessively and opens the generator breaker, or even results in flame-out of the gas turbine, then I would suggest some of the protective relay settings need to be checked and adjusted to prevent that, maybe even tripping the generator breaker open proactively.
Hope this helps!