MARK VIE COMMUNICATION FAULT WITH EX2100 EXCITER

We have GE FRAME 9E TURBINE with MARK VIE controller , problem is communication lost with exciter ex2100 that leads to fail to transfer between M1 &M2 and no responding for any command to ex2100 from cimplicity HMI
hent: Ip ping is ok for M1 &M2
 
Try with going online from ToolboxST and see if they are in controlling state?
If not, its better to get help from OEM, instead of creating further damage.
 
Try with going online from ToolboxST and see if they are in controlling state?
If not, its better to get help from OEM, instead of creating further damage.
Hello
Thank you for replying
What do you mean by controlling state,for Exciter or for MARK VIE?
 
Since we are talking about exciter issue, look into the exciter's controller.
Technically the same controller hardware is used for both Turbine controls & Exciter controls.
Some models carry additional expander carrier board for Exciter.
 
Since we are talking about exciter issue, look into the exciter's controller.
Technically the same controller hardware is used for both Turbine controls & Exciter controls.
Some models carry additional expander carrier board for Exciter.
Almost it's in the same controller Mark vie
Could you lead me to some possible solves..thanks
 
It would help to know what communication protocol your system is using between the Mark VIe and the EX2100. From what you’ve described, it sounds like the Mark VIe was upgraded, but the EX2100 was not, and I’ve seen communication issues arise when newer controllers interface with older excitation systems.

A few things to check:

  • When communication is lost, what does the EX2100 itself display? It should generate fault codes or status messages that point toward the cause.
  • In ToolboxST, what does the Exciter status show at the moment communication drops? Any alarms, loss‑of‑link indicators, or invalid data flags would be useful.
  • Even though IP ping works for M1 and M2, that only confirms network reachability—not that the application‑level communication is healthy.
  • We’ll need more information about the network topology, protocol type, and any recent configuration changes.
If you can provide the EX2100 fault list and the ToolboxST status indications, we can narrow this down quickly.
 
It would help to know what communication protocol your system is using between the Mark VIe and the EX2100. From what you’ve described, it sounds like the Mark VIe was upgraded, but the EX2100 was not, and I’ve seen communication issues arise when newer controllers interface with older excitation systems.

A few things to check:

  • When communication is lost, what does the EX2100 itself display? It should generate fault codes or status messages that point toward the cause.
  • In ToolboxST, what does the Exciter status show at the moment communication drops? Any alarms, loss‑of‑link indicators, or invalid data flags would be useful.
  • Even though IP ping works for M1 and M2, that only confirms network reachability—not that the application‑level communication is healthy.
  • We’ll need more information about the network topology, protocol type, and any recent configuration changes.
If you can provide the EX2100 fault list and the ToolboxST status indications, we can narrow this down quickly.
The protocol communication between MARK VIe and Ex2100 called EGD (ETHERNET GLOBAL DATA) , I don't think that we've upgraded MARK VIe,but may be someone changed some configurations.
The exciter alarm list itself is clear,and the exciter is ready to start in cimplicity HMI, but there is one alarm in MARK VIe "communication lost between MARK VIe and Exciter"
The specific issue is the measurements of Exciter are shown in MARK VIe,but there are no manual commands and Auto adjusting from MARK VIe to exciter
In brief, what are called "external signals" in the exciter toolbox like "voltage raise and lower,transfer between M1, & M2 , fault reset" don't reach to exciter.
Thanks for your interest
 
Since ping to M1 and M2 is OK, the network itself is fine, so the issue is most likely at the communication or service level. It’s usually caused by the EX2100 communication task being stopped or hung, EGD/OPC services in Mark VIE not running or out of sync, a redundancy issue between M1 and M2, or a configuration mismatch (IP, node, or EGD settings). Check that the EX2100 is in RUN and then restart the communication services on Mark VIE (no full reboot)
https://en.wikipedia.org/wiki/Excitation_system?
 
Since ping to M1 and M2 is OK, the network itself is fine, so the issue is most likely at the communication or service level. It’s usually caused by the EX2100 communication task being stopped or hung, EGD/OPC services in Mark VIE not running or out of sync, a redundancy issue between M1 and M2, or a configuration mismatch (IP, node, or EGD settings). Check that the EX2100 is in RUN and then restart the communication services on Mark VIE (no full reboot)
https://en.wikipedia.org/wiki/Excitation_system?
Thank you
I think you have good details about this subject,
We have tried all these steps , but as you said it's about EGD settings
Does "put into SDB" in MARK VIE THEN DO "GET FROM SDB"IN EX2100 may be useful?, because the specific issue is by the external signals from MARK VIe to exciter like "voltage raise lower, transfer between M1 M2...etc"
When we forced the signals like "voltage raise" in Mark vie toolbox, It dosn't reach to exciter toolbox.
 