HelloTry with going online from ToolboxST and see if they are in controlling state?
If not, its better to get help from OEM, instead of creating further damage.
Almost it's in the same controller Mark vieSince we are talking about exciter issue, look into the exciter's controller.
Technically the same controller hardware is used for both Turbine controls & Exciter controls.
Some models carry additional expander carrier board for Exciter.
The protocol communication between MARK VIe and Ex2100 called EGD (ETHERNET GLOBAL DATA) , I don't think that we've upgraded MARK VIe,but may be someone changed some configurations.It would help to know what communication protocol your system is using between the Mark VIe and the EX2100. From what you’ve described, it sounds like the Mark VIe was upgraded, but the EX2100 was not, and I’ve seen communication issues arise when newer controllers interface with older excitation systems.
A few things to check:
If you can provide the EX2100 fault list and the ToolboxST status indications, we can narrow this down quickly.
- When communication is lost, what does the EX2100 itself display? It should generate fault codes or status messages that point toward the cause.
- In ToolboxST, what does the Exciter status show at the moment communication drops? Any alarms, loss‑of‑link indicators, or invalid data flags would be useful.
- Even though IP ping works for M1 and M2, that only confirms network reachability—not that the application‑level communication is healthy.
- We’ll need more information about the network topology, protocol type, and any recent configuration changes.