The GCV of the Fr5 twin shaft unit we have here is hunting, the above prioblem has appeared ever since the control system has been upgraded to MKVI from MKIV.
We are suspecting the problem from the MKVI panel itself as we have tried changing the servo valve, the actuator assembly and even the LVDT's but couldn't succeed in stoping the hunting of the valve.
The above hunting is not affecting the operation of the turbine and the speed of the HP shaft is almost stable, the only problem is in the fluctuation of the pressure after the GCV and the intervalve pressure the above both are fluctuating by around 1-2 bar and the GCV valve itself is hunting by around 4-5%, whereas the SRV is hunting less compared to GCV, the frequency of the above hunting is very slow if we trace the feedback of the GCV valve it will be like a small wave.
I would like to trouble shoot into some of the parameters of the MKVI panel which is directly going to control the above servo valves like the regulator gain which is set at 3, the dither amp which is set at 2.
Seeking expert advice before to touch the above parameters also would like to know whether the above parameters can be modified in the field.
Thanks in advance,
Brian
[email protected]
We are suspecting the problem from the MKVI panel itself as we have tried changing the servo valve, the actuator assembly and even the LVDT's but couldn't succeed in stoping the hunting of the valve.
The above hunting is not affecting the operation of the turbine and the speed of the HP shaft is almost stable, the only problem is in the fluctuation of the pressure after the GCV and the intervalve pressure the above both are fluctuating by around 1-2 bar and the GCV valve itself is hunting by around 4-5%, whereas the SRV is hunting less compared to GCV, the frequency of the above hunting is very slow if we trace the feedback of the GCV valve it will be like a small wave.
I would like to trouble shoot into some of the parameters of the MKVI panel which is directly going to control the above servo valves like the regulator gain which is set at 3, the dither amp which is set at 2.
Seeking expert advice before to touch the above parameters also would like to know whether the above parameters can be modified in the field.
Thanks in advance,
Brian
[email protected]